    How do you reduce the discharge temp
    on a low temp condenssor?


    any help?

    thank you

    coolhye

  2. #2
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes


    By lowering the suction gas temperature.


  3. #3
    Join Date
    Sep 2004
    Posts
    159
    Post Likes
    coolhye,

    If you seek to reduce discharge temperature on a system with normal/acceptable return gas temperatures (such as would exist on a low temp R-22 system, there are liquid injection valves avialable for that application.

    These valves are connected to the liquid line and meter in small amounts into the suction line just upstream of the compressor's inlet in response to discharge temperature.

    You need to know what temp you want to limit the discharge temperature to, and all the regular info about your specific system and compressor.

    Go to your local wholesaler and they should be able to help you.