  1. #21
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Has this evaporater ever seen "hot water " temps over 125degrees F will deform the plastic baffles and the heat transfer goes for a S?&$ and your evap temps will take a dive .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  2. #22
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    I have my profile photo trane evaporator

  3. #23
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Longtime lurker here; sds, I see in your first statement you mention automotive plant. Is this chiller on an open sump? Is there an open tank somewhere in the chilled water system, or any other way for process debris or material to get in the chill water? If so, the chiller barrel could be acting as a strainer and be clogged up with that material. This would affect water flow rate and heat transfer. Flow decreases and pressure drop increases ( think of shutting a valve ). Heat transfer decreases due to insulating effect of material on tubes and maybe even covering some tubes and preventing water from flowing over them. This could also happen if there have been recent additions or repairs made to chill water system and debris was introduced ( this is less likely to cause this much of a problem ). If this is not an open sump.... never mind . I would look at Graham's last post. I have never seen that , but from previous posts I wonder Graham has?

  4. #24
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    I open my trane evaporator and metal baffles are both European and American (ertab, ertwb, RTAA)

  5. #25
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    185
    Post Likes
    20# entering pressure sounds low to me. Where are your pumps located in relation to the chiller? How many floors is the building? Have you checked the water makeup to make sure it's working? Did you use the same pressure gauge for the entering and leaving pressure readings?

  6. #26
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    I open my trane evaporator and metal baffles are both European and American (ertab, ertwb, RTAA)


    Read page 120 of the IOM it clearly states that the evaporator is constructed using steel. copper and POLYPROPYLENE components .
    Last time I checked polypropylene was a plastic unless I was absent from science class that day ????
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  7. #27
    Join Date
    Oct 2004
    Location
    Metro ATL
    Posts
    474
    Post Likes
    Quote Originally Posted by sds5150 View Post

    It still wonder about the internal design of the evaporator. It is strange that Circuit 1 would work, but not circuit 2.
    Phisher nailed it. Circuit 2 is closer to the EWT sensor, therefore with low flow the temp drops there first.

  8. #28
    Join Date
    Jan 2011
    Location
    troy ohio
    Posts
    3
    Post Likes

    Wink FT. of water?

    Quote Originally Posted by Phisher View Post
    Your right it is "ft of water" not psid. Not the first time if spoken without thinking first.
    Its actually "ft. of head".......pd times 2.31 equals ft. of head....which allows you to find gpm....Mike

  9. #29
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    185
    Post Likes
    Quote Originally Posted by workinschlep View Post
    Its actually "ft. of head".......pd times 2.31 equals ft. of head....which allows you to find gpm....Mike
    "ft. of head" of what liquid? If the liquid is not water, then you must factor the specific gravity of the liquid. The term "head" was adopted as the industry standard when referring to pumps. I posted the flow chart from the RTAA IOM. I'll let you read it for yourself.

  10. #30
    Join Date
    Jan 2011
    Location
    troy ohio
    Posts
    3
    Post Likes
    Quote Originally Posted by Phisher View Post
    "ft. of head" of what liquid? If the liquid is not water, then you must factor the specific gravity of the liquid. The term "head" was adopted as the industry standard when referring to pumps. I posted the flow chart from the RTAA IOM. I'll let you read it for yourself.
    That is something I hadn't considered...thank you..I just found this sight and found it pretty interesting.

  11. #31
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    185
    Post Likes
    Quote Originally Posted by workinschlep View Post
    That is something I hadn't considered...thank you..I just found this sight and found it pretty interesting.
    No problem. Welcome to the site. I learn more on this site then I do in training classes.

  12. #32
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    185
    Post Likes
    workinschlep,
    Just a word of advice. Guys on this site like to check profiles for credentials before responding to posts. Update your profile and get your post numbers up so you can apply for pro membership.

  13. #33
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by Phisher View Post
    "ft. of head" of what liquid? If the liquid is not water, then you must factor the specific gravity of the liquid...
    or pudding. it could be be pudding. what IS the specific gravity of pudding? i suppose that it would depend on flavor and whether it was made of whole milk or skim....google time!
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  14. #34
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    185
    Post Likes
    Quote Originally Posted by jayguy View Post
    or pudding. it could be be pudding. what IS the specific gravity of pudding? i suppose that it would depend on flavor and whether it was made of whole milk or skim....google time!
    I don't think flavor plays a factor but milk on the other hand changes everything. Now I'm hungry for some pudding. Thanks jayguy

  15. #35
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    FOUND IT...sorta!

    Density of water: 62.43 lbs/ft^3

    Chocolate pudding: 59.631 lbs/ft^3

    from now on...let us all convert all densities into the density of chocolate pudding and confuse the crap out of everyone!
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  16. #36
    Join Date
    Jan 2011
    Location
    troy ohio
    Posts
    3
    Post Likes

    UPDATE

    I added some details to my profile....if anyone's interested...thanks

  17. #37
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    from now on...let us all convert all densities into the density of chocolate pudding and confuse the crap out of everyone!

    But what if you dont like chocolate ??????
    Why not tomato soup ????
    Or strawberry yoghurt ??
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  18. #38
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by graham View Post
    ...But what if you dont like chocolate ??????
    Why not tomato soup ????
    Or strawberry yoghurt ??
    perfectly acceptable buddy!

    but as was mentioned before...you just need to specify...like 'feet of head' or 'feet of water' or 'feet of pudding' or 'feet of tomato soup'
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  19. #39
    Join Date
    Apr 2004
    Location
    Michigan
    Posts
    295
    Post Likes
    I've got an RTUA 70 with the exact same symptoms.

    At start up, only with circuit #2, EWT at sensor drops quickly while LWT sensor doesn't change much, and it will lock out.

    There are no provisions at chiller barrell for measuring pressures. I just found the curve for the chilled water pump and am going back to take those measurements, but I have a feeling I will find the flow to be within specs, maybe even above specs.

    Pumps from and back to an open tank. There is a filter device in the line, but when I asked the maintenance man about it he said there were no bags in it, haven't been for years. The water in the tank looks like the creature from the black lagoon would be comfortable in it.

    I'm guessing at this point that the chiller barrell is fouled, or the baffles are damaged in some way. The 1/4 inch nipple off the top of the barrell on the outlet side, used for an air vent, was plugged with crap.

    Sensors read identical when neither circuit is running and temp stabilizes thru barrell.

    Is it possible that the LWT sensor may be covered in crud, slowing it's response time in relation to the EWT sensor?
    Or could a problem with the EXV or unloaders cause this on start up, maybe especially at colder ambient?

    Is there anything else, not flow related, that would cause this?

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •