    Quote Originally Posted by sds5150 View Post

    It still wonder about the internal design of the evaporator. It is strange that Circuit 1 would work, but not circuit 2.
    Phisher nailed it. Circuit 2 is closer to the EWT sensor, therefore with low flow the temp drops there first.

  2. #28
    Join Date
    Jan 2011
    Location
    troy ohio
    Posts
    3
    Post Likes

    Wink FT. of water?

    Quote Originally Posted by Phisher View Post
    Your right it is "ft of water" not psid. Not the first time if spoken without thinking first.
    Its actually "ft. of head".......pd times 2.31 equals ft. of head....which allows you to find gpm....Mike

  3. #29
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    184
    Post Likes
    Quote Originally Posted by workinschlep View Post
    Its actually "ft. of head".......pd times 2.31 equals ft. of head....which allows you to find gpm....Mike
    "ft. of head" of what liquid? If the liquid is not water, then you must factor the specific gravity of the liquid. The term "head" was adopted as the industry standard when referring to pumps. I posted the flow chart from the RTAA IOM. I'll let you read it for yourself.

  4. #30
    Join Date
    Jan 2011
    Location
    troy ohio
    Posts
    3
    Post Likes
    Quote Originally Posted by Phisher View Post
    "ft. of head" of what liquid? If the liquid is not water, then you must factor the specific gravity of the liquid. The term "head" was adopted as the industry standard when referring to pumps. I posted the flow chart from the RTAA IOM. I'll let you read it for yourself.
    That is something I hadn't considered...thank you..I just found this sight and found it pretty interesting.

  5. #31
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    184
    Post Likes
    Quote Originally Posted by workinschlep View Post
    That is something I hadn't considered...thank you..I just found this sight and found it pretty interesting.
    No problem. Welcome to the site. I learn more on this site then I do in training classes.

  6. #32
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    184
    Post Likes
    workinschlep,
    Just a word of advice. Guys on this site like to check profiles for credentials before responding to posts. Update your profile and get your post numbers up so you can apply for pro membership.

  7. #33
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,036
    Post Likes
    Quote Originally Posted by Phisher View Post
    "ft. of head" of what liquid? If the liquid is not water, then you must factor the specific gravity of the liquid...
    or pudding. it could be be pudding. what IS the specific gravity of pudding? i suppose that it would depend on flavor and whether it was made of whole milk or skim....google time!
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  8. #34
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    184
    Post Likes
    Quote Originally Posted by jayguy View Post
    or pudding. it could be be pudding. what IS the specific gravity of pudding? i suppose that it would depend on flavor and whether it was made of whole milk or skim....google time!
    I don't think flavor plays a factor but milk on the other hand changes everything. Now I'm hungry for some pudding. Thanks jayguy

  9. #35
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,036
    Post Likes
    FOUND IT...sorta!

    Density of water: 62.43 lbs/ft^3

    Chocolate pudding: 59.631 lbs/ft^3

    from now on...let us all convert all densities into the density of chocolate pudding and confuse the crap out of everyone!
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  10. #36
    Join Date
    Jan 2011
    Location
    troy ohio
    Posts
    3
    Post Likes

    UPDATE

    I added some details to my profile....if anyone's interested...thanks

  11. #37
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,882
    Post Likes
    from now on...let us all convert all densities into the density of chocolate pudding and confuse the crap out of everyone!

    But what if you dont like chocolate ??????
    Why not tomato soup ????
    Or strawberry yoghurt ??
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  12. #38
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,036
    Post Likes
    Quote Originally Posted by graham View Post
    ...But what if you dont like chocolate ??????
    Why not tomato soup ????
    Or strawberry yoghurt ??
    perfectly acceptable buddy!

    but as was mentioned before...you just need to specify...like 'feet of head' or 'feet of water' or 'feet of pudding' or 'feet of tomato soup'
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  13. #39
    Join Date
    Apr 2004
    Location
    Michigan
    Posts
    295
    Post Likes
    I've got an RTUA 70 with the exact same symptoms.

    At start up, only with circuit #2, EWT at sensor drops quickly while LWT sensor doesn't change much, and it will lock out.

    There are no provisions at chiller barrell for measuring pressures. I just found the curve for the chilled water pump and am going back to take those measurements, but I have a feeling I will find the flow to be within specs, maybe even above specs.

    Pumps from and back to an open tank. There is a filter device in the line, but when I asked the maintenance man about it he said there were no bags in it, haven't been for years. The water in the tank looks like the creature from the black lagoon would be comfortable in it.

    I'm guessing at this point that the chiller barrell is fouled, or the baffles are damaged in some way. The 1/4 inch nipple off the top of the barrell on the outlet side, used for an air vent, was plugged with crap.

    Sensors read identical when neither circuit is running and temp stabilizes thru barrell.

    Is it possible that the LWT sensor may be covered in crud, slowing it's response time in relation to the EWT sensor?
    Or could a problem with the EXV or unloaders cause this on start up, maybe especially at colder ambient?

    Is there anything else, not flow related, that would cause this?