    May 2009
    hot water boiler Sulfuric Acid Condensation Risk
    curious to know if anyone has seen the impact to boiler from keeping a hot water boiler temperature below the sulfuric condensation temp (ie around 140).
    facility uses a large hot water boiler and keeps the boiler at 130 degrees (return is 115) - and not water treatment. the boiler manufacturer recommends keeping return temps higher than 140.
    my guess is there is beading/sweating in system that might be causing corrosion.
    ashame because they have a mixing valve and therefore would not cost much to raise water temp of boiler
    thanks for any feedback
    Mar 2001
    If the boiler isn't operated to mfg. spec. - no warrantee = $$ for repair /replacement. As you said, easy to do, but maybe too late?
    Central NH
    Damage will Result
    If your temps are too low and condensation results, you will damage the boiler. The only question is how bad they have damaged the block of that boiler. Your best bet is to pull the burner and look, maybe you will get lucky and this one will live. Time for replacement.
    Mar 2010
    Morgan Hill Ca.
    Quote Originally Posted by zeppy View Post
    If the boiler has a three way mixing valve, the energy cost to run it hotter would be extremely minimal compared to the repair cost to the boiler running it all sweaty...
    No brainer IMHO.
    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.
    Jun 2008
    Atlanta, Ga
    Depends on the type of boiler but I have seen just a couple thousand dollars damage to a ruined boiler in just three years.