Results 1 to 13 of 13

Thread: coleman furnace

  1. #1
    Join Date
    Jan 2003
    Posts
    27
    Post Likes
    I went on a service call today & homeowner said that furnace would come on & run for @ 30 seconds & then shut off.The furnace is going through the complete cycle 1.The IBM is coming on 2.the HSI is coming on 3. the burners are lighting & running for @ 30 seconds & then the furnace is shutting off. I checked the ground on the furnace,the high limit, the pressure switch & tubing,& all were ok. I will say that once when the IBM was cycling on is when it did this. Any help would be appreciated!

    Coleman-Evcon furnace- Model#BGU 075 12A
    Serial#981165134

  2. #2
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    Does this person have a supply vent blowing right at the stat? 30 seconds sounds pretty short. what was the temp. rise?

  3. #3
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Did you try pulling the stat off its subbase and jumping R to W to see if the burners stayed lit longer than 30 seconds?
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  4. #4
    Join Date
    Jan 2005
    Location
    Gilroy, Calif
    Posts
    188
    Post Likes
    Did you try to jumper the pressure switch and if so does it stay running? Problems with Inducer fan or vent piping? Spider web in portal holes? After ignition sometimes they fail due to combustion and the inducer fan can't sustain enough vacuum to hold the sw closed. Also Coleman Evcon has a recall. Was that one of the model numbers?


    [Edited by gje1 on 01-18-2005 at 12:12 AM]

  5. #5
    Join Date
    Nov 2004
    Location
    Naples, Fla.
    Posts
    1,401
    Post Likes
    And the heat anticpator is set to ___?

    When the unit cycles down, do you still have control voltage to the control center?

  6. #6
    Join Date
    Jan 2003
    Posts
    27
    Post Likes
    Thread Starter
    I didn't check the pressure switch to see if it was holding. Can you just jump across the 2 wires on the switch with a jumper wire to check it? Also after the unit cycles off I still have voltage to the board.

  7. #7
    Join Date
    Nov 2003
    Location
    Sun Valley, CA
    Posts
    129
    Post Likes
    jump C to NO on Psw will close the NO sw. You can also try sucking on the tube yourself leading to Psw and see if burners stay lit to rule out Psw. You can also check what pressure you are getting with a magnehelic and see if it corresponds with the Psw.

  8. #8
    Join Date
    Jan 2005
    Location
    Gilroy, Calif
    Posts
    188
    Post Likes
    Yes you can put a jumper across the terminals on the pressure switch. If the unit stays running than you'll have to diagnose is it the pressure switch or a problem with the inducer fan or vent piping. I'm only a Gas Serviceman for Pacific Gas and Electric Company. I visit this site to read and learn more about the industry. When I read about your problem it seemed all too familiar what I find in the field. I have only seen an inducer fan (blading) once. It was plastic and very cheaply made. The products of combustion have a lot of crap in it. The housing for the fan was extremely corroded with deposits. I digress, so what ever you have to check, per manufactures specification, vacuum from the inducer fan and airflow out of the inducer fan that will help you decide. Is it the vacuum switch or is it the inducer fan/ vent piping restricted.

    P.S. I hope you just don't start changing parts. That's not fair to the customer or the profession. With the proper tools and proper knowledge no problem can be overcome.

  9. #9
    Join Date
    Nov 2003
    Location
    warren,mi.
    Posts
    616
    Post Likes
    Flame sensor.

  10. #10
    Join Date
    Jun 2002
    Location
    Bemidji, Mn
    Posts
    3,573
    Post Likes
    Rusted out chimney, flame sense loss... Mark it.
    You picked a fine time to leave me loose wheel...

    http://rapalaguy.spaces.live.com/

  11. #11
    Join Date
    Feb 2004
    Location
    southern illinois
    Posts
    5,743
    Post Likes
    had kind of same problem today with unit installed a couple days ago........every once in a while the inducer motor would make humming sound like bearings or something......tightened screws that hold it in place and took cover off and checked for blockage....although i didn't pull the little inducer motor...it just happens every once in awhile is the thing.i am betting bad bearings....gonna dig deeper.this unit even had new style of pressure switch and new roof jack.....it has small pitch to roof on this modular home.........has anybody else had this problem?

  12. #12
    Join Date
    Sep 2004
    Posts
    3,157
    Post Likes
    have you gone to the Colman website and read about the colman-evcon recall ?

  13. #13
    Join Date
    Oct 2004
    Posts
    15
    Post Likes


    check the flame sensor or the flue , there might be a birds nest at the top.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •