heatilator direct vent
having a problem with the flame lifting off the thermopile and going out. works fine when the glass is off as soon as i put it on 20 seconds later it starts at the first openings in the burner,right by the pilot. thought air intake right away pulled everything apart looks clear, short vent 1- 90 5' total length
any suggestions?
-
11-21-2010, 02:18 PM #2
Professional Member
- Join Date
- Nov 2010
- Location
- Nevada
- Posts
- 38
-
11-24-2010, 09:23 PM #3
Regular Guest
- Join Date
- Nov 2010
- Location
- ohio
- Posts
- 10
i am new here
hello i just wanted to ad that sigguy is right , i actually had one doing that . i removed the termination cap and noticed the inner flue for the exhaust was not sealing properly leaving a gap causing the mixture. be sure the term is not clogging .