Results 1 to 2 of 2
    Nov 2010
    Maintain CFM set point
    HI,
    I was thinking on how this systems from EBM can increase or decrease the motor rpm due to maintain the cfm set point when the duct impedance increase or decrease.
    http://www.youtube.com/watch?v=zuUDAVwg1Ys&NR=1
    I saw that they are using a static pressure sensor but how they can manage the motor speed with the pressure?
    Thank you!
    Fort Worth, TX
    Quote Originally Posted by Domia View Post
    HI,
    Thank you!
    I didn't watch the video, but can say that variable speed blower operation is done all the time by static pressure setpoint. The static pressure is measured by a transducer, which converts pressure to an analog electrical signal. A controller is then programmed to respond to this signal (the signal could be 4 to 20 milliamp or 0 to 10 volts DC) and send a similar signal to the variable frequency drive (VFD) which then ramps up or down according to what is needed to hold the static pressure setpoint.
    To maintain a consistent cubic feet per minute (CFM) setpoint would likely involve a different type of design than what I described above, which is commonly used for systems employing variable air volume boxes (VAV) in various zones throughout the building. With what I described above, the CFM will vary in order to maintain a constant static pressure.
    Building Physics Rule #2:
    Building Physics Rule #3: