Thread: Please help, freezing refrig line in add-on cooling

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Join Date
    Jan 2005
    Posts
    8
    Post Likes

    Question

    Hi,

    We have an add on cooling unit to our central heating. It's a Pioneer, 3 phase, 19kw unit. The house is approx. 32 squares. The heating and cooling is zoned separtely upstairs and downstairs. There is a return air vent both upstairs and downstairs. The whole system, and house, are only 3 years old. The thermostat is a Brivis Networker.

    The problem is, the larger of the two copper refrigerant pipes from the indoor coils to the outdoor unit that is covered with foam insulation(I think it's the suction line) becomes frozen because the refrigerant is being forced back to the outdoor compressor. When this happens, the copper pipe freezes up like a balloon, and the indoor temperature keeps rising. The whole air conditioner stops cooling, even though the fans and compressor keep running, and the whole system just wastes electricity.

    If the air conditioner has not been used much (ie, if there haven't been many hot days during summer), it fires up and works perfectly. However, the pipe seems to freeze whenever it's been working hard during the day, and there's a drop in outdoor temperature (such as a cool change, common in Melbourne Australia during the summer). The outside temperature will drop, inside temperature in the house will rise from about 23 degrees C to 25 or even 26 degrees C. The compressor will continue to work all night, with the pipe frozen, and the temperature will not drop unless it's significantly colder outside (yeah, I know this wastes money, but it's uncomfortably hot to sleep at night).

    Furthermore, if the unit has been working all night with the pipe frozen, and hot weather has been forecast for the remaining few days, the a/c will continue to struggle, and the pipe will remain frozen (I guess because the unit hasn't been off long enough for the refrigerant to unfreeze).

    Now for the interesting part - the a/c company who installed the system cheated on us and installed non-genuine Pioneer coils in the roof, without our knowledge or permission . We only found out when another a/c repair company inspected the coils in the roof. And of course, that same a/c company has gone bankrupt (I wonder why), no longer exist, and of course we now have no warranty .

    Some other information -

    - The first repairman was "not so smart", and reversed the polarity on the compressor, and over-filled the unit with freon, so the compressor would pop and bang when switched on, and not run at all.

    - The second repair company, sent by the builder, fixed the above, and drained and re-filled the unit again with freon. But ever since he did this, the pipe has been freezing even worse, and the cooling problems became worse. The cooling capacity was always suspect, and the pipe would always freeze to some extent, but not as badly as it has done last summer and this summer.

    - The second repairman fitted a thermostatic expansion valve (TXV) near the compressor on the outdoor unit. We both thought this would fix the problem, but when he hooked up his guages to the unit, it still did weird things, like working perfectly for 5 minutes, before sending refigerant back to the compressor again, and freezing the pipe, and then unfreezing and working perfectly again after a few more minutes.

    I have been reading the following website to try and diagnose the problem, but my knowledge of a/c units is limited :
    http://www.longviewweb.com/coolfix.htm

    In summary, considering all of the above, I can only conclude :

    a) The unit is overcharged with refrigerant. Perhaps both repairmen are incompetent, and are not sure what the correct amount of refrigerant the unit requires.

    b) There are not enough return air grills in the house for the unit. Less likely, imo, as the unit cools adequately unless the pipe is frozen, as described above.

    c) The non-genuine indoor coils are incompatible with the Pioneer outside unit.

    d) The whole compressor and outdoor unit are screwed, and need to be taken out the ocean and attached to a anchor and chain

    Any advice would be appreciated

  2. #2
    Join Date
    Mar 2004
    Location
    NJ
    Posts
    1,212
    Post Likes
    Some of your statements have to be seriously wrong especially the one about the TXV location....Either way it sounds like atotal mess plus a few different "techs" seem to have all tinkered with it which makes it hard if someone new comes out but what I would like to know what temperature are you setting the system at 80 degrees F? 75 degressF?sorry celsius is not my gig.
    thehumid1-------I live in NJ, a state where it's free to come in but you have to pay to leave!

  3. #3
    Join Date
    Jan 2005
    Posts
    8
    Post Likes
    Thread Starter
    The inside temp on the thermostat is never set below 22 degrees C / 71 degrees F.

  4. #4
    Join Date
    May 2003
    Location
    Dixie
    Posts
    1,352
    Post Likes
    filter dirty, coil dirty, low on ref. to name a few....find yourself a compentent tech

  5. #5
    Join Date
    Jan 2005
    Posts
    8
    Post Likes
    Thread Starter
    Thanks for your help.

    The filters in the return air vents are not dirty. They are cleaned regularly. Both techs went into the ceiling and said the coils weren't dirty. Is incompatible coils the answer, or is there not enough airflow to the unit (ie, not enough return air vents) ? Is there any way to adjust the fan speed to the return air vents ?

    Could there be any reason why the system is blocking excessively with ice now ? It's only been worse after the second tech filled with freon. The pipe has always frozen to some extent since day one, but not to the extremes it is now, and before the techs touched it, the system still cooled even if the pipe was a little frozen.

    Thanks !

  6. #6
    Join Date
    Mar 2004
    Location
    NJ
    Posts
    1,212
    Post Likes
    It should never freeze and 71 degree setpoint on 100 degree F day in the outback isnt going to happen but there are way too many variables for me to even suggest what the problems are... starting from what seems to have been a bad install to the other info given find someone competent like was said.
    thehumid1-------I live in NJ, a state where it's free to come in but you have to pay to leave!

  7. #7
    Join Date
    Nov 2004
    Posts
    98
    Post Likes
    when you get someone to look at it have them recheck the amount of refrigerant,expansion valve,and make sure the evaporator fan is working.also make sure the sensing bulb is installed correctly.if that dont work visit your inlaws for a while.

  8. #8
    Join Date
    Jun 2001
    Location
    San Diego, CA
    Posts
    1,265
    Post Likes
    This is not a problem with a simple solution. The entire system needs to be evaluated. If it's a good design, any good technician will fix it easily. If it's not a good design, he'll tell you that too.

    Could be a fan problem, could be a refrigerant problem. Could be the components are mismatched, could be the TXV is not adjusted or installed properly. Could be there's air in the system. All of these need to be considered and any tech worth a bag of hammers will check all of this and find the problem.

  9. #9
    Join Date
    Jan 2005
    Posts
    8
    Post Likes
    Thread Starter
    Techs were back again today.

    I showed them a copy of the Pioneer a/c installation sheet I had lying around from when the unit was purchased. Seems that the liquid line is smaller than it needs to be. Spec sheet says half a inch, the line running to the ceiling is smaller. The installers welded a smaller liquid line to the half inch pipe inside the a/c condensor unit.

    They will come back next week and replace the liquid line and fit a TXV next to the condensor unit.

  10. #10
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Originally posted by losiho
    Hi,

    We have an add on cooling unit to our central heating. It's a Pioneer, 3 phase, 19kw unit. The house is approx. 32 squares.
    I think you lost most of us at that point.

    What is a "square"?
    What capacity in BTU's would 19kw translate to?

    Most of us on this forum are in north America and have no experience with the equipment you have. Hopefully one of the Brits or someone will be along soon and have some ideas for you.

  11. #11
    Join Date
    Apr 2004
    Posts
    10
    Post Likes
    I think we are all in serious need of more data to be able to help. If I had to guess, your system is suffering from a lack of airflow. An expansion valve maintains a specific amount of superheat so with a low airflow situation the superheat will drop. This will cause the valve to close off even more thereby dropping the suction pressure which lowers the saturation temperature of the refrigerant well below freezing and it only gets worse after the coil starts to frost up, it is a vicious cycle that snowballs (no pun intended) the longer the system runs. I would like to know what the temperature split is across the evaporator, superheat, subcooling, pressures, etc. Also, what type of refrigerant??? R-22???

  12. #12
    Join Date
    Jan 2005
    Posts
    7
    Post Likes
    what kind of ref is in this system maybe r22 with a 410a exp?
    had that happen before. works great till you get a hot day!

  13. #13
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    Originally posted by mark beiser
    Originally posted by losiho
    Hi,

    We have an add on cooling unit to our central heating. It's a Pioneer, 3 phase, 19kw unit. The house is approx. 32 squares.
    I think you lost most of us at that point.

    What is a "square"?
    What capacity in BTU's would 19kw translate to?

    "Square"=10ft. by 10ft.=100sqft.=3200sqft.
    A term mostly used by roofers.Metric might be different.

    1 watt=3.41 btu
    19 kilowatt=64790btu

  14. #14
    Join Date
    Jan 2005
    Posts
    8
    Post Likes
    Thread Starter
    The liquid line was replaced today (the original copper pipe was undersized) and a TXV valve fitted in the roof next to the coils.

    The unit is filled with R22.

    Forgive me if my explanations sound pathetic, I'm no a/c expert, and I only have basic knowledge of this stuff (although at times I belive the "techs" know about as much as I do )

    I will correct my first post here, the tech installed an accurator to the system the first time around, it did not have a TXV installed until today.

    Today, after the system was turned on after installing the pipe and valve, the techs filled the system with R22. They filled it until the sight glass was clear (yeah I now know this is wrong, I just read another thread here). The suction pipe inside the outdoor condensor was still starting to frost after a short time, so a tech went in the ceiling to adjust the TXV. Now I don't know how to read or understand a vacuum gauge reading, but one tech at the condensor unit was reading the temps to the guys upstairs adjusting the TXV. It started at about -12 degrees C (10 degrees F) and they adjusted it to between -5 and -6 degrees C (23 - 21 degrees F). The temperature coming out of the air vents was 12.5 degrees C (54 degrees F). Inside temp according to the thermostat was 24C (75F) and outside temp was about the same. After the techs adjusted the TXV, the suction pipe inside the condensor did not frost up.

    Well, about 1 hr after the techs left, and the unit had been running, the suction line again freezed up almost as bad as it had been before ! As usual, the inside temp stays at around 23 -24C (73 - 75F).

    I've thrown my hands up in the air, I'm totally confused. The techs said that the coils are clean and that "this was not the problem anyway".

  15. #15
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    [QUOTE]Originally posted by jacob perkins
    Originally posted by losiho
    1 watt=3.41 btu
    19 kilowatt=64790btu
    Duh! I knew that, just am not used to thinking in KW for cooling, thanks.

    Surely a "square" in a country that uses the metric system isn't the same as a "square" here is it?




  16. #16
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    Originally posted by losiho
    a) The unit is overcharged with refrigerant.


    Not likely, as more refrigerant RAISES the temperature of the coil.
    If anything, it could be undercharged.
    This is NOT the only problem, and modifying the charge will NOT resolve the problem.

    Perhaps both repairmen are incompetent, and are not sure what the correct amount of refrigerant the unit requires.

    Apparently self-evident. Replace them.

    b) There are not enough return air grills in the house for the unit. Less likely, imo, as the unit cools adequately unless the pipe is frozen, as described above.


    This is like saying "It works great until it quits. So it must not have a problem? Right?"

    What do you think CAUSES the frozen pipe?

    This is a MOST likely contributor, as airflow dictates how much heat reaches the refrigerant.

    Airflow is CERTAINLY VERY HIGH on the list of things that MUST BE VERIFIED.
    Simply visually inspecting a coil does not prove it is clean. Pay somebody to take it out & CLEAN it.
    Has anybody actually measured the airflow?
    I don't mean hold your hand in front of the grill.
    I mean MEASURED.
    Cubic Feet Per Minute (CFM), or liters per second?

    The indoor FAN may be inadequate, too. Is it clean?

    c) The non-genuine indoor coils are incompatible with the Pioneer outside unit.

    This is a possibility that must be ruled out. I have no way to do that from here. Find a competent contractor. Contact the manufacturer, if need be. Replace it, if necessary.
    If it is incompatable, it is a sizing issue.

    d) The whole compressor and outdoor unit are screwed, and need to be taken out the ocean and attached to a anchor and chain
    THE PROBLEM IS NOT IN THE OUTDOOR UNIT.
    Unless it is a sizing issue.
    It is suffering, and may be dying, but the indoor section, plus ductwork, is where the problem lies.
    I cannot imagine that you are in such a remote part of the world that there are no competent individuals available.

    Get off your wallet and pay somebody to do it right.


    [Edited by bwal2 on 02-11-2005 at 09:05 AM]
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  17. #17
    Join Date
    Jan 2005
    Posts
    8
    Post Likes
    Thread Starter
    To all the people who suggest a lack of airflow or dirty coils, could they please try to give an explanation as to why the system will work perfectly without freezing on some days, and others it will freezing the suction pipe to a block of ice and not cool at all ? There is no consistent pattern to its operation - there have been really hot days where the a/c has worked perfectly and will not freeze at all, and other milder days where it will freeze totally and not cool.

    I'm not trying to be a smarty pants or question anyone's knowledge, just trying to help you (hopefully) help me with my problem !

  18. #18
    Join Date
    Jul 2002
    Location
    Zelienople, Pa
    Posts
    2,965
    Post Likes
    Maybe you have a dingo stuck in the accumulator tension bearings?

    LOL!
    How tall are you Private???!!!!

  19. #19
    Join Date
    Dec 2004
    Posts
    201
    Post Likes
    maybe you shouldnt run the a/c when its only 75 degrees out,,,you shouldnt need it any way,,my answer is not enough load

  20. #20
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    Originally posted by losiho
    To all the people who suggest a lack of airflow or dirty coils, could they please try to give an explanation as to why the system will work perfectly without freezing on some days, and others it will freezing the suction pipe to a block of ice and not cool at all ? There is no consistent pattern to its operation - there have been really hot days where the a/c has worked perfectly and will not freeze at all, and other milder days where it will freeze totally and not cool.

    I'm not trying to be a smarty pants or question anyone's knowledge, just trying to help you (hopefully) help me with my problem !
    The load that your air conditioner must move is heat.
    Heat flows toward cooler objects.
    The indoor coil is, by design, cooler than the air that passes over it.
    It is also designed to remove water from the air.
    The indoor coil must run cool, but not cool enough to form ice from that water, because ice will restrict airflow.
    Airflow is critical.

    The conditioner can't condition something it doesn't touch.

    Air conditioners, unlike food storage equipment, are designed to NEVER freeze up. This is done, among other things, by controlling the boiling point of the refrigerant. Defrost is expensive.
    The temperature of the coil is directly related to the heat contained in the air.
    Not just the temperature of the air, but the total heat, taking into account that water vapor contained in air, also contains heat.
    On a cool day, the air is cooler (less heat).
    There is simply not enough heat in the air, on a cool day, to keep the coil above the freezing point of water.

    Normally, an air conditioner is not run on cool days, so extra engineering & controls are not necessary.

    Yours is not working properly, so the temperature does not have to be very cool to send the indoor coil & connecting piping below freezing.

    Which end of the island are you on?
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •