Page 1 of 2 12 LastLast
Results 1 to 13 of 16
  1. #1
    Join Date
    Jun 2003
    Location
    GA
    Posts
    395
    Post Likes

    Question

    I'm not an easy sell for rules-of-thumb, left unqualified they can be conditionally true or an oversimplification of a concept lost or watered down. Anyway let me run this one up the flag pole.

    *** HGT = 126 + ambient ***

    (1) This a good one?
    (2) Can you also say HGT = 126 + RA DB for a Heat Pump in Heat Mode?
    (3) I've read of charging by HGT (scary), but even if true it would have to be under some base line, induced ARI, or peek demand conditions. I'm not willing to set or adjust change by HGT alone and then walk w/o looking and SH and SC to complete the picture.
    (4) Most importantly, can HGT = 126F + {ambient/RA}DB be used as secondary information to confirm other indications of charge or heat exchange problems?
    (5)Anybody know the basis for this rule-o-thumb? Lift? CR? Specific volume? PFM??

    TIA,

    md

  2. #2
    Join Date
    Nov 2002
    Location
    emerald city, sc
    Posts
    1,469
    Post Likes
    a properly charged and operating compressor adds 126° of heat.
    i wanted to put a picture here

  3. #3
    Join Date
    Jul 2001
    Location
    Delaware
    Posts
    1,232
    Post Likes
    Originally posted by tlcartman
    a properly charged and operating compressor adds 126° of heat.
    If a properly charged & operating compressor adds 126Ί of heat, should we not be measuring the temperature of the compressor suction line & adding that figure to the 126 instead of adding ambient? Not trying to be argumentative, just trying to learn more about heat pumps since I seem to be stuck working on the @#$%^&* things lately.
    Work is for people who don't know how to fish.

  4. #4
    Join Date
    Dec 2004
    Location
    Belton, Texas
    Posts
    107
    Post Likes
    I think one of the real experts needs to jump in here and discuss the terms 'heat' and 'temperature'. I think some confusion is brewing over the use of these terms.

  5. #5
    Join Date
    Jun 2003
    Location
    GA
    Posts
    395
    Post Likes
    Thread Starter

    Talking gona catch hell for this

    Thank you, that would work for me.
    and don't water it down to were it makes no sense. LOL

    Is it to be found in (PV/T)=(PV/T), the combined gas law.

    If so,

    T2 = T1(P2/P1)(V2/V1), but V.E. is never 100% so,

    T2 = T1(P2/P1)(V2/V1)(V.E.) if compression is adiabatic.

    Oh, yeah...
    T2 - 75F is what you would measure about 6" out says Copeland.

    I'll pay around with that and look up some Copeland V.E. charts and see if I can find any loose agreement with HGT = 126+ ambient.

    md

  6. #6
    Join Date
    Jun 2003
    Location
    GA
    Posts
    395
    Post Likes
    Thread Starter
    bump

  7. #7
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    if subcooling and superheat are correct then hgt will always be correct. remember subcooling tells you if your system has the proper amount of refrigerant and superheat tells you if there is any problems with your system and how much superheated vapor is returning from evap coil so trying to charge refrigeration systems with your guages only, rules of thumb are basically out of the question with all the differant efficient systems now or any other method is usually not a safe or viable practice.

  8. #8
    Join Date
    Jul 2001
    Location
    Delaware
    Posts
    1,232
    Post Likes
    We are not talking about a Rule of Thumb. The hot gas method is the specified method by at least one manufacturer. If other parameters do not fall in line, there is some other problem as well.
    Work is for people who don't know how to fish.

  9. #9
    Join Date
    Apr 2004
    Posts
    106
    Post Likes
    I have been using that rule of thumb for years as a quick check and it has never let me down!

  10. #10
    Join Date
    Jan 2002
    Posts
    137
    Post Likes
    How about suction pressure in the heat mode equal to outdoor temp. for a close charge. Anyone heard of that one before? How about amp draw? Anyone heard of that either ? i have always heard that superheat method is best and proper.

  11. #11
    Join Date
    Oct 2004
    Posts
    146
    Post Likes

    charging by outside air temp

    Originally posted by Keith Lohr
    How about suction pressure in the heat mode equal to outdoor temp. for a close charge. Anyone heard of that one before? How about amp draw? Anyone heard of that either ? i have always heard that superheat method is best and proper.
    I have done that a few times, it was pretty cold and had to use a bucket of hot water to charge unit... Seems to be ok with me, havent heard of any call backs or so... ill have to write down some pressures on my next changeout.

  12. #12
    Join Date
    Jul 2001
    Location
    Delaware
    Posts
    1,232
    Post Likes

    Talking More food for thought or fuel for the fire

    IF ambient + 126Ί works for heating, why not cooling?
    Work is for people who don't know how to fish.

  13. #13
    Join Date
    Sep 2004
    Posts
    51
    Post Likes

    Question HGT

    Originally posted by whitepoundog
    I have been using that rule of thumb for years as a quick check and it has never let me down!


    Just trying to gather info for using HGT as a diagnostic tool. First off why and how do you use discharge gas temp and what does it tell you? Do you take this reading first or do you measure your subcooling or superheat first? Do you add the OAT or the R/A.