Results 1 to 8 of 8
Thread: Controls: Very Basic Question
11-15-2010, 11:11 PM #1
New Guest
- Nov 2010
- 4
New to the field, is this a true statement? If I have a Constant Air Volume (CAV) system, then is it always true that the OA damper and RA damper are linked together to maintain constant air volume (i.e., as the OA damper opens, the RA damper closes)?
And, related to this question, if a packaged unit delivers air at a constant volume, can I assume the OA and RA dampers came already provided from the manufacturer and already set-up to behave this way?
11-15-2010, 11:22 PM #2
- Oct 2010
- 17
Yes most all osa damper and ra damper are linked together. In most small cav they share the same actuators. A packaged unit econmizer in most cases will be will require some assembly but the osa and ra damper should be set-up. However check with the install manual there are some settings on the econmizer that may need to be set.
11-16-2010, 02:39 AM #3
- Jun 2006
- Athens Greece
- 108
In my area it is very hard to identify a standard from unit manufacturers provisions..
Just inspect the unit's mixing box, and try to identify damper actuators (one-two or three), in case there are less that three (OA, RA mixing) check for an assembly that connects them...
Try to move manually the actuator(s) and check the rotation of the mixing box...
Simple as stealing a kids candy...!!!
11-16-2010, 04:45 PM #4
- Jun 2009
- StL, MO
- 532
That could easily be a trick question. A constant air volume unit can also be 100% outdoor air.
UA LU 562
11-16-2010, 04:59 PM #5
Permanently Removed
- May 2002
- 9,564
No.
11-16-2010, 06:37 PM #6
Professional Member*
- Mar 2009
- Several Miles from Sane
- 1,401
If sense were so common everyone would have it !
All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!
11-16-2010, 08:12 PM #7
- Oct 2005
- 309
It's not that common on a CV unit but the OA could be controlled separately based on CO2 control.
11-18-2010, 04:03 PM #8
No, not always. Many times it's done with direct linkage cause it's cheaper & easier. Think about controlling building pressure as well. You can get better control by controlling return and and OA separately. Open the OA damper enough to help keep the building pressure positive, but leave the RA damper in the full return air open position until you start economizing, then start backing off the RA damper after the economizer signal gets greater than the OA damper min. position. Granted typically w/many man hours one could adjust the linkage as such to do what I am suggesting, but it is very difficult.
Most of the time yes, but not all the time. You can special order package units to behave almost however you desire. Also on larger units you normally will see separate actuators due to torque requirements.
http://en.wikipedia.org/wiki/Glossary_of_HVAC"How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
http://threedevilskennel.com/ - not my website.