    Combustion air

    I just had a Rheem Elite system installed. I kept hearing water and waves in the morning and knew the PVC lines were holding water. I have about 12-18 inches of 2 inch pipe on each end but most of the run is 3" for about 12 horizontal feet. They were not pitched toward the furnace for drainage at all. I called them back and they lowered the inside exhaust line about 4 inches (dumping 2 gallons) but not the intake line. When I asked why not both lines the technician claimed no need? Is this true?
    Also I live in SE Pennsylvania and it is not unheard of to have 2-3 feet of snow, even more against my house on the deck. I am nervous if I leave for a couple days and snow builds up over the lines it will shut down freezing pipes and my pet. The technician claimed I can not raise the outdoor lines more or it will add too much resistance? The outside portion is not glued to allow me to adjust it but he just barely fit 2" pipe through the wall. Need I be concerned about this? See Photo attached. What is proper? Thanks
    http://www.flickr.com/photos/38738791@N07/5163340697/

  2. #2
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    normaly you can get by not pitching combustion air. the manuals say do it. you are allowed only so much pipe and so many elbows you might not have any allowance to rase the termination. then again it is 'sposed to be 12" above expected snow level

  3. #3
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,743
    Quote Originally Posted by claudius2k View Post
    I have about 12-18 inches of 2 inch pipe on each end but most of the run is 3" for about 12 horizontal feet. http://www.flickr.com/photos/38738791@N07/5163340697/

    are the 2" X 3" reducers on each end of the 3" pipe in a horizonal or vertical pipe?

    reducing couplings should never be in horizonal pipe.

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,090
    Quote Originally Posted by t527ed View Post
    are the 2" X 3" reducers on each end of the 3" pipe in a horizonal or vertical pipe?

    reducing couplings should never be in horizonal pipe.
    Unless they are offset reducing couplings.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,743
    Quote Originally Posted by beenthere View Post
    Unless they are offset reducing couplings.
    i have never seen that type of fitting until another thread i was reading the other day had a sketch of one....

    will have to look for them next time i'm picking up fittings, they could come in handy.

  6. #6
    Join Date
    Apr 2008
    Location
    Pluto
    Posts
    983
    Quote Originally Posted by t527ed View Post
    i have never seen that type of fitting until another thread i was reading the other day had a sketch of one....

    will have to look for them next time i'm picking up fittings, they could come in handy.
    When asking for them, just remember that fittings of those type are called eccentric couplings.
    Not as lean, not as mean, but I'm still a hardcore, ass-kicking, hard charging Marine! Oohrah!

  7. #7
    well one reducer is on the vertical 12 inches above the furnace, the other is horizontal a few inches before exiting the outside wall. However that is how the manufacturer's installation guide pictured them.

    Thanks

  8. #8
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,743
    sounds like you should be ok with the reducers where they are. moisture is not usually a problem in the air intake.

    i would be concerned about how low your terminations are with the possible snowfall in our area raising them a couple feet would not cause that much resistance.

  9. #9
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,281
    Here in my area I don't believe you are allowed to vent a condensing furnace out on to a deck. Something about the byproducts of gas, gassing you while you're on the barbecue or something else in the cooler months like I do?

  10. #10
    Join Date
    Nov 2008
    Location
    Altamont, IL
    Posts
    379
    Rheem/Ruud requires a trapped drain fitting in the horizontal combustion piping near the furnace. You don't want the condensation getting into the furnace. Any condensation in the exhaust line should run to the furnace and down the drain.
    In GOD We Trust

  11. #11
    Thank you JdWendling. That is pretty much how I assumed it should work. Thanks for confirming.