    Smart Valve Mystery

    We tried to start up a N9MP105 furnace today for temp heat. The furnace has a smart valve SV9541M2094 with ST9160 EFT.

    The furnace was converted to propane last year and was working.

    Now the ventor motor comes on, the ignitor glows but the pilot never gets any gas. We tried 2 smart valves, 1 board and one ignitor. Still no gas.

    We have 11" WC at the gas valve. No blockage in the pilot tubing.

    We installed the propane spring in the new smart valve we tried.

    The ventor motor is coming on. We tried jumping the PS after the ventor starts just in case we have having an problem with it.

    We tried coming out all the limits and safeties. Still not gas will flow out of the valve.

    The only thing we probably don't have is a good ground. But this should cause the pilot valve not to open?

    Any suggestions would be great.

  2. #2
    Join Date
    Mar 2004
    Location
    Illinois
    Posts
    6,959
    I have several suggestions but can not post them in the open forum. Get your post count up and apply for pro membership.

    There is much more available that you can not see...

  3. #3
    Join Date
    Nov 2010
    Posts
    12
    Thanks Senior Tech

    I have a lot of experience with York products. I have been in a service department for 8 years.

  4. #4
    Join Date
    Nov 2010
    Posts
    12
    But this smart valve has me stumped and an unhappy customer

  5. #5
    Join Date
    Mar 2004
    Location
    Illinois
    Posts
    6,959
    Good...you should have no problem qualifying for pro membership.

    http://hvac-talk.com/vbb/forumdisplay.php?f=38

  6. #6
    Ya could have bought a new furnace for the cost of all them parts.
    Keep changing em till it works I guess.
    Hey cockroach, don't bug me! ©

    www.AskTheDiceman.com

    www.TheColdConspiracy.com

    www.Pennwood-HVAC.Com

    Bring Em Home....

  7. #7
    Join Date
    Nov 2010
    Posts
    12
    Found the problem. I had a bad regulator on the propane tank. I got 10 IWC intially but it increased after I took off the manometer. The ignitor was coming on but I guess if there is too much gas pressure the pilot wont open. Once I was able to get a steady 10 IWC it open and the pilot lite every time

  8. #8
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,832
    hmmmmmmmmmmm?
    never had that happen before!

    I have had it decrease after running, but never increase?





    Quote Originally Posted by JCR View Post
    Found the problem. I had a bad regulator on the propane tank. I got 10 IWC intially but it increased after I took off the manometer. The ignitor was coming on but I guess if there is too much gas pressure the pilot wont open. Once I was able to get a steady 10 IWC it open and the pilot lite every time
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,952
    Quote Originally Posted by JCR View Post
    But this smart valve has me stumped and an unhappy customer

    We look forward to seeing you in the Pro area. Welcome!
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  10. #10
    Join Date
    Oct 2009
    Location
    new jersey
    Posts
    240
    The smart valve is not smart. I check flame sensor ma on other sensors. Can u check it w/ out cutting wire?

  11. #11
    Join Date
    Nov 2009
    Location
    Saskatchewan
    Posts
    492
    I know EXACTLY what is doing that! Last week I was on the phone to tech services.I called them back and told them what it was and that were WRONG as to their ideas.

  12. #12
    Join Date
    Nov 2009
    Location
    Saskatchewan
    Posts
    492
    It is so simple a Cave Man could......... LOL

  13. #13
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,024
    Quote Originally Posted by JCR View Post
    Found the problem. I had a bad regulator on the propane tank. I got 10 IWC intially but it increased after I took off the manometer. The ignitor was coming on but I guess if there is too much gas pressure the pilot wont open. Once I was able to get a steady 10 IWC it open and the pilot lite every time
    Thanks for posting the solution.
    Beware of advice given by some guy on the Internet.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event