  1. #14
    Join Date
    Oct 2001
    Location
    LONG iSLAND,NY
    Posts
    13
    I did have heat the entire time I had the problem with short cycling. The only time I personally hit the reset was after I changed the filter. Once I touched the filter I couldn't get the burner to run continuously.By then I knew oil flow was the problem. If this occurs again, I assume I can take my air hose to the oil line to blow it out. Right?


    steve

  2. #15
    Join Date
    Jul 2001
    Location
    Delaware
    Posts
    1,232
    No, not right. If it happens again & probably if it does not, the lines & maybe the tank need replacing. That sludge is coming from somewhere, probably the tank.
    Work is for people who don't know how to fish.

  3. #16
    oil-2-4-6-gas is offline Professional Member b&M _email server rejected
    Join Date
    Aug 2003
    Posts
    294

    .

    you might have yourself an even bigger problem if you get your compressor and you use too much pressure --anyway if your tank is over 30 years indoors its time to clean it-have it tested, replace the valve,lines, pitch the tank--if underground that age its time to remove it