Liebert Model CM60AF-15-Y-OHP
Have a 10 ton HVAC unit supporting a computer room on and military base in South Korea. Alarms are "Loss of air flow" and "Overtemperture" Sure overtemperature will ocur with no air flow.-- Filters are clean, blower drive belts and wheels are in good shape-- I think the problem is with the small pc board with the single sensor on it. "Senser Board-- Part number 0617222. Here is the problem-- this unit was made in Australia and the factory closed and went to China. Assuming this is the problem, Where can I get a new board?
-
11-08-2010, 01:28 AM #2
Regular Memeber
- Join Date
- Jul 2010
- Location
- Andalucia
- Posts
- 3,210
"War is cruelty,and you cannot refine it." Sherman to the leadership of Atlanta prior to burning the city.
"Common sense is the collection of prejudices acquired by age eighteen."
Albert Einstein
Romney campaign: "We're not going to let our campaign be ruled by fact-checkers,"
Lindsey Graham: Were not generating enough angry white guys to stay in business for the long term.
-
11-11-2010, 08:43 PM #3
Sounds like dirty air filters!
The alarm looks for differential across the return, which incorporates the filters and indoor fan suction.
Dirty filters would result in "Loss of Cooling" which would result giving over temperature alarm.Dealing with Global Warming
-
11-12-2010, 07:06 AM #4
Banned
- Join Date
- Dec 2006
- Location
- Middle Tennessee
- Posts
- 11,347
*
i would not blame the board right away
you probably have a faulty sail switch
double check it for open/close/stuck circuit
.