    I was looking for a LON interface to a Multistack but didn't find one.

    I see the ALC BACnet portal, but since the customer wants to purge their ALC stuff that's a no-go.

    Anybody go a different route with these units?

  2. #2
    Looks like BACnet is it, have you contacted them?

  3. #3
    Join Date
    Feb 2002
    Posts
    180
    Sysint, I can be of absolutely no help to you. But can you explain something to me? What is ALC and what is meant by purging it?Hope this isnt a reeeally stupid question.Im trying to learn more about DDC and networking.Picking up what I can where I can. Also is this a Carel contoller. I've seen multistack uses carel in their chillers with turbocor compressors. Thanks for any info.

  4. #4
    Join Date
    May 2002
    Posts
    9,564
    787- ALC "Automated Logic Corporation"

    By "purging" I mean that they can't stand their ALC stuff and want to get rid of it all.

    They just re-badge this controller for use as a gate. I will check into this Carel controller.... so I guess you are helping already. It may be that this Carel controller is some ASCII or Modbus controller, in which case I wouldn't need the ALC Portal. (which is probably a gateway to BACnet.

  5. #5
    Join Date
    Nov 2004
    Location
    North Florida/South Georgia
    Posts
    984

    Smile wait for me!!!!

    I'm worse off than the 787 Guy. You guys are brilliant, I think. What I mean is, as a wrench turner I have a hard time following. But, I'll keep reading & hopefully I'll be able to pick up on a thing or two.
    All my leon freaked out!

  6. #6
    Join Date
    Feb 2002
    Posts
    180

    Talking

    thanks for clearing that up for me. The answer wasn't any where near as technical as I thought it would be




  7. #7
    Join Date
    May 2002
    Posts
    9,564
    Well - called Multistack directly.

    Apparently they are completely unaware of what you can do with Lonworks and think there is a point restriction.

    I suppose if you are using an ALC BACnet Portal that would be the response.

    At this point I don't know if they are uninformed, lazy, or BACnetisized past reason.

    I do know they aren't getting any military jobs anytime soon. Lonworks only....

    Gave them a reference for a LON controller interface up to 4000 points. That should be more than enough for their little chiller. Until then it's Fieldserver - or spec another chiller.


  8. #8
    Join Date
    May 2004
    Location
    Caldwell, ID
    Posts
    395
    Is this an air or water cooled multi-stack? Actually the air cooled models are called "airstack". The AC and Turbocor models use the Carel Pco2 controller.

    The pco2 has a LON card available (I have used it), but multistack has to write the code for the controller to work with it. It is not just a matter of popping in a card.

    The nice thing of the LON interface for the Pco2 is it is just a card that plugs into the obody of the controller. With modbus, BACnet, and the other gateways, you have to use a serial card that plugs into the body that is then wired into the gateway.

    If this is not a Carel powered chiller, then fergit it, can't help.

    Clyde

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event