    2 Thermostats in 1 Zone?

    Is it possible to put more than one thermostat in a zone? I’d like to keep providing heat until all thermostats are above their set point and keep providing cooling until all thermostats are below their set point. A really fancy might know to up the fan speed if the difference between the thermostats became large. I know commercial systems work kind of this way. Is it ever done for residential?

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Not really. You can get a thermostat that uses remote sensors. And have them installed in different areas of that zone. And then average the temps of all of those sensors.

  3. #3
    Join Date
    Sep 2010
    Posts
    23
    Post Likes
    Thread Starter
    It seems like this would be easy to do with an old mercury thermostat. If it is hot enough the circuit is open and if it gets cool the thermostat closes the switch to call for heat. If you hooked two of these together in parallel, when either switch closed, the circuit would close and the heat would come on.

    I know the thermostats are a lot fancier now, but is the communication with the heater really more sophisticated?

  4. #4
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    Post Likes
    it can be done. in some ways it is easier with the new stats as the anticipators don't factor. but it can be easy to get both the heat and cooling on at the same time. that is not very efficient.

  5. #5
    Join Date
    Sep 2010
    Posts
    23
    Post Likes
    Thread Starter
    Yes, but the humidity would go down

    How is this done. Do you need special thermostats or can you hook up regular ones this way?

  6. #6
    Join Date
    Sep 2005
    Location
    Murrieta CA
    Posts
    10
    Post Likes

    Stop and look

    Step back and look at what has been done!! Tel the coustomer NO unless after looking at whats been done the second stat has a remote sensor and is only mounted in the other zone because of looks. That could be whats up or you could be under attack from THE HANDYMAN !! LOL just step back and think it through, remember to fix something you gotta know how it is supposed to work.
    Goodluck - Warmaire

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by David Lang View Post
    It seems like this would be easy to do with an old mercury thermostat. If it is hot enough the circuit is open and if it gets cool the thermostat closes the switch to call for heat. If you hooked two of these together in parallel, when either switch closed, the circuit would close and the heat would come on.

    I know the thermostats are a lot fancier now, but is the communication with the heater really more sophisticated?
    Mercury thermostats use a heat anticipator. Connecting the stats in parallel. Will cause short cycling when both call at the same time.

    A digital using remote sensors won't have that problem. Nor will there be a problem that someone sets one stat too high or too low. Since all the temp settings are done from one unit.

  8. #8
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    Post Likes
    Quote Originally Posted by beenthere View Post
    Mercury thermostats use a heat anticipator. Connecting the stats in parallel. Will cause short cycling when both call at the same time.

    A digital using remote sensors won't have that problem. Nor will there be a problem that someone sets one stat too high or too low. Since all the temp settings are done from one unit.
    other way isnt it? 1/2 the current through each- long cycle? if only one calls then you get a normal cycle? unless youset it to short cycle on one any way does not matter with digital stats. but there are lots of ways to screw it up.
    dont do it unless you know how. and if you know how you know not to do it.

    the remote aveaging stat is good. not real simple or cheap

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by fearlessfurnace View Post
    other way isnt it? 1/2 the current through each- long cycle? if only one calls then you get a normal cycle? unless youset it to short cycle on one any way does not matter with digital stats. but there are lots of ways to screw it up.
    dont do it unless you know how. and if you know how you know not to do it.

    the remote aveaging stat is good. not real simple or cheap
    No. 2-1500 ohm resistors wired in parallel equals 750 ohms.

  10. #10
    Join Date
    Nov 2010
    Location
    NC
    Posts
    23
    Post Likes
    Not sure your reason for doing this and I could be wrong, but if you did hook up the two tstats wouldnt you have considerable overheating/overcooling of the stat that satifies first? The temperature between the two stats will never be right unless you split the ductwork up and zone it properley.

  11. #11
    Join Date
    May 2007
    Posts
    779
    Post Likes
    Quote Originally Posted by beenthere View Post
    Mercury thermostats use a heat anticipator. Connecting the stats in parallel. Will cause short cycling when both call at the same time.
    If each stat has the anticipator set as if there were only one stat, when both call there would be less anticipator effect (half the amperage through each anticipator assuming equal resistance). When one thermostat stops calling the anticipator of the one still calling would become normal. But, the one that satisfied first would cool down and start calling sooner than it would have if it's anticipator had been working normally. But, that might be offset by the overheating of the space by the other thermostat.

    And what about the cooling anticipator on mercury stats? Since they function during the off cycle when the mode switch is set to cool, having two in parallel will lengthen the cycle (half the amperage, less heating, longer time to initiate a call).

    If the boss said I had to wire two thermostats in parallel, first I'd say "really?" then...

    Relay logic to prevent either stat from operating in an opposing mode. So, if a stat is in cooling mode (may or may not be calling for actual operation) the other stat heating mode is locked out, and so on. Would take two relays for each stat and one extra wire at the stat. Some stats may not have the appropriate terminal for this function.

  12. #12
    Join Date
    May 2007
    Posts
    779
    Post Likes
    Quote Originally Posted by beenthere View Post
    No. 2-1500 ohm resistors wired in parallel equals 750 ohms.
    Heat circuit amperage is a fixed value, not dependant on the anticipator value. With two equal paths, amperage in each path will be half.

  13. #13
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    Post Likes
    you see it done around here in newly finished basement situations (forced air)works ok even with T87Fs. were things get screwy is if you try to do the heat and AC through both stats. real easy to get the heat and cool both running.

  14. #14
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    Post Likes
    Quote Originally Posted by MR FIX IT View Post
    Not sure your reason for doing this and I could be wrong, but if you did hook up the two tstats wouldnt you have considerable overheating/overcooling of the stat that satifies first? The temperature between the two stats will never be right unless you split the ductwork up and zone it properley.
    yep

  15. #15
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    Post Likes
    Quote Originally Posted by fxb80 View Post
    If each stat has the anticipator set as if there were only one stat, when both call there would be less anticipator effect (half the amperage through each anticipator assuming equal resistance). When one thermostat stops calling the anticipator of the one still calling would become normal. But, the one that satisfied first would cool down and start calling sooner than it would have if it's anticipator had been working normally. But, that might be offset by the overheating of the space by the other thermostat.

    And what about the cooling anticipator on mercury stats? Since they function during the off cycle when the mode switch is set to cool, having two in parallel will lengthen the cycle (half the amperage, less heating, longer time to initiate a call).

    If the boss said I had to wire two thermostats in parallel, first I'd say "really?" then...

    Relay logic to prevent either stat from operating in an opposing mode. So, if a stat is in cooling mode (may or may not be calling for actual operation) the other stat heating mode is locked out, and so on. Would take two relays for each stat and one extra wire at the stat. Some stats may not have the appropriate terminal for this function.
    the cools are ok they are getting straight 24V ac. the current on the heat side is regulated by the valve or relay (whatever) so the same current goes through 1 or 2 stats depending.
    Last edited by fearlessfurnace; 11-09-2010 at 07:39 PM. Reason: added "t" to stas

  16. #16
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    Post Likes
    Quote Originally Posted by beenthere View Post
    No. 2-1500 ohm resistors wired in parallel equals 750 ohms.
    on the cool. ok each stat has about .016a just like always

  17. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by fxb80 View Post
    Heat circuit amperage is a fixed value, not dependant on the anticipator value. With two equal paths, amperage in each path will be half.
    Meaning that the anticipator. Won't heat up as much, so it will come back on quicker. Giving short off cycles.

  18. #18
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    Post Likes
    Quote Originally Posted by beenthere View Post
    Meaning that the anticipator. Won't heat up as much, so it will come back on quicker. Giving short off cycles.
    heat anticipator comes on with the heat warming the stat and speeding up the "off"
    less antipator less stat warming-longer cycle.

    cool anticipator heats the stat during the off cycle (cool of is kinda sorta like heat "on"). it gets full 24 volts and does not need to be adjustible.
    Last edited by fearlessfurnace; 11-09-2010 at 07:51 PM. Reason: put "L" in vots

  19. #19
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by fearlessfurnace View Post
    heat anticipator comes on with the heat warming the stat and speeding up the "off"
    less antipator less stat warming-longer cycle.

    cool anticipator heats the stat during the off cycle (cool of is kinda sorta like heat "on"). it gets full 24 volts and does not need to be adjustible.
    Less heat mean shorter off time. So it short cycles.

  20. #20
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    Post Likes
    Quote Originally Posted by beenthere View Post
    Less heat mean shorter off time. So it short cycles.
    no you set the anticipator to match the amp draw. cut the draw in half now the anticipator is set to high .02a is at the "short" end 1.0a is at the "long" end. its called an anticipator because it anticipates the heating of the house and turns the furnace off. or am I thinkinf backwars?? NO I AM NOT. I think

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •