Better to replace a check valve than a compressor
The primary function of the check valve is to stop the reversal of flow causing the rotors to free wheel in reverse when the gas re-expands after a compressor shutdown in order to prevent damage from the thrust reversal.
A second but equeally important function of the check valve is to prevent refrigerant condensing and draining into the compressor during an off cycle. Refrigerant will migrate to the coldest area and in the liquid state is influenced by gravity.
In applications like the RTAA where the compressor is below the condenser, if the check valve is not sealing refrigerant could fill the compressor during the off cycle and cause problems ranging from high motor starting current to compressor damage from the hydrostatic forces developed by the screws pumping 100% liquid.
My advice is if the check valve is leaking change it out or you will be asking the customer to pay for a compressor replacement in the immediate future.
-
11-15-2010, 07:25 PM #28
and the rest of the story.,
anyways ., ordered the chcek valve, the following day i called to check in on something else., talked to same guy and he asked me if c valve was on top of compressor., said no ., he faxed over spec sheet., he was going to order me oil system c valve,
got right KIT coming., (kit02308)
support c valve,
o ring
washer c valve.,
retainer c valve
seal c valve.,
and this should do the trick.,,..,no signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
11-17-2010, 07:35 AM #29
am i wrong?
am i wrong to say and do this?.,,,
when accessing the discharge end of the compressor to change check valve, piston and rings that the discharge line will need to be unbolted and cut downstream of the discharge line shut off valve,and moved out of the way., that is the only way i see able to have any room to work on one of these areas.,.,
trane screw
rtaano signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
11-17-2010, 09:37 AM #30
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 865
You should be able do bend it out of the way.
-
11-17-2010, 09:44 AM #31
Professional Member
- Join Date
- Mar 2010
- Location
- Va.
- Posts
- 178
Buy the suction valve gasket. Isoltate the compressor. Unbolt the suction and discharge lines. Slide the compressor on the base rail enough to clear the discharge line. If you cut the line you will still have a hard time putting the coupling on unless you can find a slip coupling.
-
11-17-2010, 11:26 AM #32
-
11-17-2010, 07:10 PM #33
-
11-17-2010, 07:23 PM #34
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 865
The RTAA's above 130 tons have an oil line solonoid on each compressor. When the compressor shuts down, the UCM de-energizes the oil solonoid before the compressor shuts down to verify that the oil differential switch trips within a certain amount of time. If it doesn't, the UCM calls out an oil safety fault.
-
11-17-2010, 07:36 PM #35
-
11-17-2010, 09:36 PM #36
there's not much room, but it can be done...just takes skinny fingers to get the gasket areas clean.
cperk is funny...2,2 dichloro-1,1,1-trifluoroethane!The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
11-18-2010, 12:23 AM #37
suction gasket all day
thanksno signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
11-18-2010, 07:50 AM #38
Professional Member
- Join Date
- Mar 2010
- Location
- Va.
- Posts
- 178
Hey mlkwal1 I'll be down your way the 1st of Dec for a long weekend.
-
11-18-2010, 05:59 PM #39
Let me know when u get in town
no signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!



Reply With Quote