    gram and ga1279 I bet if the 2 of you were standing in front of a screw at shutdown you would both agree on what sounds normal and what sounds abnormal. It sounds like your interpreting what mlkwal1 is describing as a strange noise at shutdown differently. Just my unbiased opinion.

    mlkwal1 you need to find some other screw machines and listen to them when the compressors cut off to get a better feel for what sounds normal. If in doubt I would rather replace the check than the compressor.

  2. #15
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    very well said phisher.,actually when the other compressor shuts down , it just stops., and i was working on an rtaa 80 ton and those screws just shut down and turn off., no noise .,., but when a trane screw does turn backwards, obviously there is a problem, and most likely it is the check valve.,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  3. #16
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    180
    There should be a distinct sound when the check closes. Put the circuit into a manual pump down. If the check valve is holding then you should maintain a pressure difference between the condenser and evaporator. Have you checked the oil solenod on the oil supply line to make sure it closes when the compressor cuts off? I'm not sure if that can cause the compressor to back spin or not but it might be something to check. Any ideas on that?

  4. #17
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,063
    Ok let me try to expand on what is normal . Chiller running normal conditions , chiller goes into pumpdown compressor shuts off . for about 1 or 2 seconds at the most you will hear a groan or moaning sound followed by a slap as the check valve closes then silence . if this is what you are hearing , no problems . if you are hearing a continuous moan and no slap then yes you have check valve issues .
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  5. #18
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    875

    The backward sound

    No, I'm not talking about my golf game. The backspin of the screws is a pretty definite sound. I have replaced many bad checks out there, my wife says I'm just under deposited. Graham keep us posted on your "Green Machine"-GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  6. #19
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,317
    Quote Originally Posted by ga1279 View Post
    If the rotors on a GP compressor are allowed to backspin they will put an opposing thrusting force and eventually cause rotors to make contact. I don't think Trane change their guidelines from the mid-nineties. The development engineer for the smaller RTAA's 70-125 ton said there should no back-spinning of the rotors on shutdown. It could go bang, pop slap itself around a few times but never turn in reverse. There was a notice to this problem passed out during the early Pueblo classes, (memo not a service bulletin) -GEO
    First of all, the RTAA140 doesn't have GP compressors, it has intermediate compressors.

    It doesn't hurt the compressor to backspin for a short amount of time on shutdown as a result of pressures equalizing. The thrust is still against the thrust bearing when the presssures are equalizing. As a matter of fact, the RTHC and RTHD compressors don't have a 100% sealing check valve and they will roar for several seconds on shutdown. It is bad however, for a screw compressor to be powered running backwards as there is no thrust bearing on the opposite side of the rotors.

  7. #20
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    Nope has chunk compressors .. check valve is most definitely bad. When I shut down circle 1 . Back spins for about 5 seconds. Sounds like a jet engine. And I don't hear the slap. When I shut down circle 2 .I hear the slap and the compressor shuts off..
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  8. #21
    Join Date
    Sep 2004
    Posts
    175
    Check Valve it is.

  9. #22
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,720
    Quote Originally Posted by graham View Post
    Ok let me try to expand on what is normal . Chiller running normal conditions , chiller goes into pumpdown compressor shuts off . for about 1 or 2 seconds at the most you will hear a groan or moaning sound followed by a slap as the check valve closes then silence . if this is what you are hearing , no problems . if you are hearing a continuous moan and no slap then yes you have check valve issues .
    Man we used to have a guy that would go around condeming the 2-3 second back spins and for some reason I would have to do the work. Always pissed me off when the customer was now smart enough to listen when the compressor shut off. I agree that if pressures equalize pretty quickly from back spin on a screw that the check valve should be replaced.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  10. #23
    Join Date
    Mar 2007
    Posts
    3,108
    There is a lot of information floating around out there about these mystical screw compressors. Who knows what to believe?

    Is the discharge check valve there to isolate the refrigerant in the condenser when the machine is off, is it there to prevent reverse rotation, or both?
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  11. #24
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    Quote Originally Posted by BergerMech Rob View Post
    There is a lot of information floating around out there about these mystical screw compressors. Who knows what to believe?

    Is the discharge check valve there to isolate the refrigerant in the condenser when the machine is off, is it there to prevent reverse rotation, or both?



    Going backwards
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  12. #25
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    309
    Reading this post I think back to the first of the RTHB chillers we started out here in 94. In the early days of the screws the official company position was "no service work inside the compressor" replacement was the only option. From the first shutdown on this chiller you could here the slap of the check valve but then the screws would rotate backwards for the next 10-12 seconds while the compressor groaned and the chiller vibrated.

    Obviously a leaking check valve but following much discussion with compressor engineering we were advised the decision was ours to replace the check valve, replace the compressor or leave as it was and run it until the compressor failed. Management made the call and the compressor was left as it was.

    You know it is now 16 years later, this original untouched compressor has well over 60,000 hrs of service and yes still spins backwards for the same time every shutdown.

    But I would still agree with the advice in this post, if the check valve is leaking then it should be changed out.

  13. #26
    Join Date
    Feb 2010
    Posts
    81
    RTAA I assume you have more than one compressor on this chiller, do nothing , let it run , if it blows then you know it was a screwy sound.

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event