    Can I use a passive louvered grille for O.S.A. to a 300 sq. ft. office? How many cfm per sq. ft. of grille?

    Thanks,
    Mike

  2. #2
    Join Date
    Jun 2004
    Location
    Florida
    Posts
    556
    You can use a louver to provide natural ventilation in Florida. The free area must be 4% of the floor area. You would want to size the louver for the free area and not the CFM. In your case you would want a louver with a free area of 12 sq/ft. That's a large louver. Are there any operable windows in the building? Maybe you can get credit for those. I have never seen anyone use this code before though.

    http://www.sbcci.org/Florida_Buildin...0sec%20402.pdf