Results 1 to 5 of 5
  1. #1
    Join Date
    Nov 2010
    Posts
    2
    Post Likes

    Kitchen heat load

    Hi,

    Can u please advice whether to consider the heat loads which is coming under a proper Kitchen hood, while selecting the AC equipment.

    I am working on a design of a small size take-away restaurant outlet,(420 sq. feet area).
    Excluding the burners under the hood, the HAP load estimate is coming to 3 Tons, 1400 CFM.

    But, if i am including the burners, then it goes to 7.5 Tons,4400 CFM.

    OR, only a portion of the burner heat load to be considered?

    Any leads will be highly appreciated

  2. #2
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301
    Post Likes
    Reference thread Pizza shop load calculation under this forum heading as I discussed this issue at length

  3. #3
    Join Date
    Jan 2008
    Location
    Lake Worth, FL
    Posts
    111
    Post Likes

    Talking

    Also in most areas of the country makeup air is required. That will reduce the heat load and save on A/C tonnage

  4. #4
    Join Date
    Nov 2010
    Posts
    2
    Post Likes
    Thread Starter
    Thank you both, for the leads

  5. #5
    Join Date
    Jul 2007
    Location
    New Jersey
    Posts
    3,035
    Post Likes
    Isnt a 3 ton system 1200 cfm, unless its heat pump. Heat pumps are usually 450 cfm per ton. And 1400 cfm makes 466 cfm per ton.
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton


    I'm learning all the time, the tombstone will be my diploma!!!


    Did you ever stop to think, and forget to start again?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.