    Hi,
    Can u please advice whether to consider the heat loads which is coming under a proper Kitchen hood, while selecting the AC equipment.
    I am working on a design of a small size take-away restaurant outlet,(420 sq. feet area).
    Excluding the burners under the hood, the HAP load estimate is coming to 3 Tons, 1400 CFM.
    But, if i am including the burners, then it goes to 7.5 Tons,4400 CFM.
    OR, only a portion of the burner heat load to be considered?
    Any leads will be highly appreciated
    NE Alabama
    Reference thread Pizza shop load calculation under this forum heading as I discussed this issue at length
    Lake Worth, FL
    Talking
    Also in most areas of the country makeup air is required. That will reduce the heat load and save on A/C tonnage
    Nov 2010
    Thank you both, for the leads
    New Jersey
    Isnt a 3 ton system 1200 cfm, unless its heat pump. Heat pumps are usually 450 cfm per ton. And 1400 cfm makes 466 cfm per ton.
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
    I'm learning all the time, the tombstone will be my diploma!!!
    Did you ever stop to think, and forget to start again?