    Kitchen heat load

    Hi,

    Can u please advice whether to consider the heat loads which is coming under a proper Kitchen hood, while selecting the AC equipment.

    I am working on a design of a small size take-away restaurant outlet,(420 sq. feet area).
    Excluding the burners under the hood, the HAP load estimate is coming to 3 Tons, 1400 CFM.

    But, if i am including the burners, then it goes to 7.5 Tons,4400 CFM.

    OR, only a portion of the burner heat load to be considered?

    Any leads will be highly appreciated

  2. #2
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301
    Reference thread Pizza shop load calculation under this forum heading as I discussed this issue at length

  3. #3
    Join Date
    Jan 2008
    Location
    Jackson, MI
    Posts
    111

    Talking

    Also in most areas of the country makeup air is required. That will reduce the heat load and save on A/C tonnage

  4. #4
    Thank you both, for the leads

  5. #5
    Join Date
    Jul 2007
    Location
    New Jersey
    Posts
    3,031
    Isnt a 3 ton system 1200 cfm, unless its heat pump. Heat pumps are usually 450 cfm per ton. And 1400 cfm makes 466 cfm per ton.
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton


    I'm learning all the time, the tombstone will be my diploma!!!


    Did you ever stop to think, and forget to start again?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event