    Just wondering if anybody can help with this question. What protects the controller from high pressure in a pneumatic control system?

  2. #2
    Join Date
    Aug 2004
    Location
    Boston, MA
    Posts
    110
    Pressure relief valve protectc devices if regulator fails.T-stats and most controllers max psi is 30 but some need 60 psi or more.

  3. #3
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,810
    60 PSI is a bit TOO HIGH for Commercial Pneumatic devices 30 PSI is the MAX that " most" devices will handle.

    Main air pressure is reduced to 30 PSI by a PRV , control air pressure depending on the manufacturer runs 13 - 22 PSI.

    On a pilot positioner for a Valve or Damper actuator you would use both the 30PSI to drive the actuator and the control pressure to operate the positioner.

    safety relief valves should be on the downstream side of any PRV to protect the system if the PRV fails or is incorrectly set.

    [Edited by Control Man on 04-14-2005 at 10:57 AM]

  4. #4
    Join Date
    Nov 2003
    Location
    Boston
    Posts
    600
    Originally posted by Control Man
    60 PSI is a bit TOO HIGH for Commercial Pneumatic devices 30 PSI is the MAX that most devices will handle.
    ???????????????????
    I have a system where a 20# line goes to "normal" devices such as thermostats and small actuators and a 60# line goes to large "Commercial" devices --Cooling tower by-pass valves, Bray valves on boiler headers etc.

    Very common applications. 20# circuit is protected by a 30# relief valve and 60# circuit is protected by 75# relief.

    Also have systems with a 100# riser and each floor has a pressure reducing station to knock the pressure down to what is required for each branch.

  5. #5
    Join Date
    Aug 2004
    Location
    Boston, MA
    Posts
    110
    I have several 60 psi devices is some of the larger buildings I service, usually a large (8 inches and up) chilled water valve or bldg deny valve requires higher psi for close off force againsed 140 psi water.Same setup as powerhead stated, 100 psi 1/2 riser (15 story bldg) with regulator/relief station at each floor with end of mains looped into itself.

  6. #6
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,810
    Your VALVES ( BRAY and 8" and up ) are not the NORMAL COMMERCIAL application type devices and the part about MOST DEVICES in my posting would cover that.

    In nearly 30 years of pneumatics very seldom ran across anything from the normal COMMERCIAL control companies operating above 30 PSI in a basic commercial installation.

    I have ran across loads of devices in central heating / chiller plants operating above 30 PSI but those are not what you would call NORMAL applications as what my post was about.

    The 30 / 20 PSI was a basic reference to a TYPICAL pneumatic system , I have systems that are 100 PSI + on the Mains and stepped down to required range throughout a 185,000 sq foot 1 storey building and others that have a 30 PSI main that supplies a 24 storey building.


    A typical BARBER COLMAN 6" 3 way valve will close off against 125 PSI Water with an actuator that takes 10 PSI , and yet a 2 way 6" will only close off against 21 PSI with a 20 PSI actuator , so you see not everything is TYPICAL

    [Edited by Control Man on 04-14-2005 at 11:10 AM]

  7. #7
    Join Date
    Aug 2004
    Location
    Boston, MA
    Posts
    110
    Exuuuuuuuuuuuse me

  8. #8
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,810

    Red face

    I posted a valid response no need for the CHILDISH reply

  9. #9
    Join Date
    Aug 2004
    Location
    Boston, MA
    Posts
    110
    U posted an insecure defence, I was just stating that there are high psi devices, but it doesnt matter because i have ony 17 years control experience so u must know more than me.

  10. #10
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,810
    Like I said no need for CHILDISH response , never disputed the fact there are HIGH PRESSURE devices just that they are RARE on TYPICAL commercial pneumatic applications.

    It was far from a INSECURE DEFENCE unlike you reference to 17 years experience and how I know more, again very childish.


  11. #11
    Join Date
    Aug 2004
    Location
    Boston, MA
    Posts
    110
    I was refering to ur previous reply stating "nearly 30 years pneumatic experience" So u started the whole "childish" thing. Also no one said anything about typical, cause whats typical for one may not be typical for another.............Im done arguing with u!!!

  12. #12
    Join Date
    Mar 2005
    Location
    South/West of Quebec in the other part of Canada
    Posts
    2,331
    maybe just to add to this I have always be curious. If air pressure is lost will the pneumatic valve fail in the open or closed position?

  13. #13
    Join Date
    Jan 2004
    Location
    New Jersey
    Posts
    534

    pneumatics

    Originally posted by key
    maybe just to add to this I have always be curious. If air pressure is lost will the pneumatic valve fail in the open or closed position?
    It depends on which type is selected and how they are applied. They can be purchased,N.C.--requires air to open,N.O.--requires air to close. these two types make up most of the typical applications.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event