  1. #1
    Join Date
    Nov 2004
    Posts
    5

    Unhappy

    I've a sick house! (I think)

    We had a new fancy variable speed furnace installed about 3 weeks ago. Since then, we've been getting up with irritated eyes (burning), cloagged up and irritated (burning) nostrils, and slightly soar throats. My little daughters cought during the night and in the morning when they wake up and have psymtoms of a cold with slight runny noses.

    Nights have been cold and the furnace has been running mostly at night. Our symptoms are mostly eliminated during the day (we have an older house that is vented pretty well through the old windows! ;0) and are totally gone about a couple of hours after we leave the house.

    We also have a humidifier and 2 Hygrometers that tell us inside humidity is at 40-42% (strangely, I have set the humidistat to around 30%).

    I've two CO deterctors and neither indicates anything abnormal.

    The contractor sent a technician back who did a visual inspection of the humidifier (ensured it is wet and water is flowing on it) and the furnace (removed the panel and looked at the flame). He then said that the problem was very likely with the air vents not having been cleaned for a long time. He suggested I get the vents cleaned and also use a better filter (I use the kind you can buy for $3-5 at home depot) to eliminate allergens. He claimed the new Infinity Carrier has a much stronger blower and that's why we had no symptoms with the old furnace.

    Does this sound reasonable?
    If so, what should we look for in a vent cleaning company?
    Anything else to worry about?

    Thank you in advance.


  2. #2
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,027
    The stronger blower thing is what I was thinking also.

    I remember and install that replaced an old belt driven drive. I went back two days later to do somthing and could of sworn that the installer never even looked at the filter because it was so dirty. The new blower just sucked the dirt right out of the return.
    Beware of advice given by some guy on the Internet.

  3. #3
    Join Date
    Feb 2004
    Posts
    2,597
    is this by any chance an attic installation. if so its possible the return is not properly sealed and it is pulling in insulation particles, distributing them throughout the ductwork.

  4. #4
    Join Date
    Apr 2004
    Location
    Lubbock, Texas
    Posts
    267
    I would definitely have my duct sealed and as for duct cleaning I have yet to see a great one but make sure you check around and if the vaccum is able to be carried in the house rather than mounted in the van send them on they’re way

    >>>edit... removed caps


    [Edited by jultzya on 11-09-2005 at 12:37 PM]
    Learning never ends and everyone has something to teach. Some people teach me what to be like others teach me what not to be like!

  5. #5
    Join Date
    Sep 2003
    Location
    Suburban Washington, DC (Maryland)
    Posts
    207
    This is where someone posts a picture of the Caps Lock key to familiarize conrad with this wonderful feature.

    Yes jonny since the humidity seems up to par I would suspect stronger blower dislodging things as well.

    You can buy filters that you cut to size and actually put behind the registers also.

    I've not been a fan of duct cleaning since I joined this board but this might be a case where it is actually indicated.

    Good luck, and keep us updated!

  6. #6
    Join Date
    Jan 2002
    Location
    Ft.Worth,Tx
    Posts
    4,584

    Unhappy Christmas Blues

    Sounds to me like everybody has sinus infections and that is from air-born particles, so that is not the furnace but ductwork and filter system.If you didn't have ducts cleaned or sized properly for the new system, here lies the problem.

    Cfm of the new furnace is greater due to design .
    Might want to have someone check all the ductwork, returns to insure they are sealed.Most new duct cleaning company's that are good will have a camera so that you can see the duct inside and find any splits,cracks or places that need to be sealed.Change your filter today, if your family is sick then the spores are inside the filter and if not changed it will only prolong there illness.

  7. #7
    Join Date
    Jul 2002
    Location
    Zelienople, Pa
    Posts
    2,965
    Originally posted by lumberg

    You can buy filters that you cut to size and actually put behind the registers also.

    [/B]
    This is the worst advice ever given on this board.

    DO NOT put filters behind your registers unless you want higher utility bills, shorter lifespan of the equipment, and the possibly to crack the heat exchanger and kill everyone in the house!
    How tall are you Private???!!!!

  8. #8
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,579

    It is possible that you still have a carbon monoxide problem. Most home co alarms will not go off until fairly high levels of co are detected. Only a low level co alarm would go off. So you may have a co problem.

    The changes made with the installation of your new furnace may actually have changed the pressure differentials in your home. If the furnace is exhausting more air up the flue there is always the possibility that a negative pressure is being created which can prevent other fuel fired appliances from venting properly. A gas water heater or even a fireplace for example.

    Have a contractor come in with a professional co analyzer such as Bacharach's Monoxor 2. Have them check each appliance for co. In addition, have them check each appliance under different conditions. Such as with the furnace on and off. With the furnace and all appliances on as well as with the bathroom and range exhaust fans on as well. Try to create a negative pressure in the house and then check the draft and co production of each fuel fired appliance.

    For more information go to: http://www.bacharach-training.com


  9. #9
    Join Date
    Aug 2002
    Location
    Westlake, Ohio
    Posts
    2,470
    Norm Chris is right on the money. Just had a lady and a couple of kids that had been experiencing the same symptoms and found her boiler making over 600ppm of CO. It was not all dumping into the house but enough to make them sick. After the contractor fixed the problem their symptoms went away. Your alarms will allow 70-399ppm in your house for hours and not go off. If the furnace is tied to a water heater it could be causing it to make CO. You really need a contractor that knows what he is doing and the one you have doesn't have a clue!
    captain CO

  10. #10
    Join Date
    May 2004
    Posts
    1,462
    Originally posted by Jim Davis
    You really need a contractor that knows what he is doing and the one you have doesn't have a clue!
    What crystal ball did you look at to determine this? Since you do not know what he did or did not do how did you reach this conclusion?
    If all else fails....Try reading the directions!

    Tell it like it is and let the chips fall where they may.

    Any views or opinions stated here are strictly my own.


  11. #11
    Join Date
    Oct 2001
    Location
    Waterford Michigan
    Posts
    2,668
    Is your home at the proper humidity level?

  12. #12
    Join Date
    Feb 2004
    Location
    Maine
    Posts
    483
    I feel that NormChris is on the right track. I assume this is a gas furnace. Gas furnaces can also produce some oxides of nitrogen which is a respiratory irritant. That could explain the sore throats, burning eyes, burning nose etc. Sounds to me like something is not venting as it should. It could also be dust blowing out of the ducts with a stronger blower, that would at least explain the stuffy nose, but burning eyes and sore throat leads me to think it's a venting issue. Any funky new smells?

  13. #13
    Join Date
    Apr 2004
    Location
    Lubbock, Texas
    Posts
    267

    CAPS LOCK

    Originally posted by lumberg
    This is where someone posts a picture of the Caps Lock key to familiarize conrad with this wonderful feature.

    Yes jonny since the humidity seems up to par I would suspect stronger blower dislodging things as well.

    You can buy filters that you cut to size and actually put behind the registers also.

    I've not been a fan of duct cleaning since I joined this board but this might be a case where it is actually indicated.

    Good luck, and keep us updated!
    SORRY to offend!!!!!!! lumberg
    Learning never ends and everyone has something to teach. Some people teach me what to be like others teach me what not to be like!

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event