Results 1 to 13 of 18
Thread: Controls Tricks of the Trade
12-21-2004, 07:32 PM #1
Hey everyone, how bout we start a thread to help out new people and old, anything from straight and simple to generic.
I saw someone post this already but
on a 4 to 20ma device you can use a 250 ohm resistor to make the device 0 to 5 VDC or 500 ohm for 0 to 10 VDC
Honeywell Modutrol Motors-Have a bunch of them that are potentiometer and you need a DC input instead? Honeywell makes a module that you can plug into the motor to change it to VDC, you can find the PDF on the module here
http://hbctechlit.honeywell.com/tech...0s/63-2235.pdf
Also Honeywell has the famous "Gray Book" you can find it here, its a big download
http://68.209.216.66/html/Training/H...llTraining.htmDad's Hideout The online mancave for dads
12-21-2004, 07:53 PM #2
- Oct 2004
- 875
Thanks for the links, good stuff.
02-07-2007, 02:08 AM #3
Banned
- Jul 2005
- 140
your grey book link is dead.
02-07-2007, 07:25 AM #4
Permanently Removed
- May 2002
- 9,564
HONEYWELL ENGINEERING MANUAL of AUTOMATIC CONTROL for COMMERCIAL BUILDINGS
....Otherwise known as the Honeywell Grey Manual.
02-07-2007, 08:12 AM #5
02-07-2007, 09:05 AM #6
- Aug 2006
- New England
- 517
Just a slight correction: 250 ohms gets you 1-5VDC. 500 ohms gets you 2-10VDC. Good ole Ohm's Law: 500*.004=2 500*.02=10on a 4 to 20ma device you can use a 250 ohm resistor to make the device 0 to 5 VDC or 500 ohm for 0 to 10 VDC
02-07-2007, 06:19 PM #7
It was 2 years ago, you can give me a break on the math
Also the Honeywell book in book form
http://store.hydronicpros.com/product.php?qcp=1028
02-07-2007, 08:51 PM #8
Why'd ya leave out the 1000ohm? That converts ma to volts directly. I've used AOs as constant DC sources before.
02-10-2007, 03:59 PM #9
Banned
- Jul 2005
- 140
in control, please explain about the 1000 Ohm set-up.
02-10-2007, 05:07 PM #10
1000ohm will turn 0-20ma to 0-20vdc
500ohm will turn 0-20ma to 0-10vdc
375ohm will turn 0-20ma to 0-7.5vdc
250ohm will turn 0-20ma to 0-5vdc
etc....
Use the formula (V = I x R)
Some controllers have a max load of 500ohms, etc... So you cant do this with everything.
Edit: almost forgot about this site -
http://www.csgnetwork.com/ohmslaw.html
Use the "To calculate the circuit voltage" (V = I x R)
So on the webpage, in the Amps field put .004 (4ma), put 500 in the Ohms field, click calculate and you get 2 volts,
etc...Last edited by codewriter; 02-10-2007 at 05:12 PM.
02-11-2007, 12:25 PM #11
Banned
- Jul 2005
- 140
transmitters and transducers?
basic question------------what is the difference between a transmitter and a transducer?
02-11-2007, 12:34 PM #12
- Dec 2006
- Hartford, Connecticut
- 440
A Transmitter would be a Field Device connected to a DDC Controller as an Analog Input Point, such as a static pressure transmitter or %RH.
A Transducer is connected to a DDC Controller on a Analog Output Point, which would modulate a signal to a Field Device. 0-10 vdc, 4-20 mA, 0-20 PSI, 0-135 ohms etc...
02-11-2007, 12:35 PM #13
They are all transducers in my mind. A transducer is an electronic device that converts "energy" from one form to another.
When it comes to pnuematics, I use the term transmitter though, it was just how I learned it back in the day.
I think a lot of people interchange this word, and most people will probably know what your talking about even if you do not use it so called "properly".