Thread: Ringing pipes

  1. #14
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,875
    Remove the service panel and see if the noise changes. If it does, then its the vent piping, if not, its the circ.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    it is probably making that noise on space heating only because the boiler starts firing on low fire on heat call, and then ramps up if needed, on a dhw call the boiler goes right to high fire. that noise will only be produced with a low air flow in the vent. ..........i think

  3. #16
    Join Date
    Sep 2005
    Posts
    73
    Yes, but the noise is present even if the boiler is not firing and the circs are still pumping.

  4. #17
    Join Date
    Mar 2002
    Location
    Gaylord, Michigan
    Posts
    729
    0011 is kind of big for the primary loop isnt it? That is a high velocity pump, at least I thought it was. Since the primary loop is generally short, I would think that using a 0011 is overkill.

  5. #18
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,875
    Some thing may have gotten into it, or it may be a defective unit.
    Its under warranty, have it replaced if defective, or the obstrution removed.



    Chris:
    The Ultra 230 requires a 0011 for the primary loop.

    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #19
    Join Date
    Jun 2003
    Location
    New Hampshire
    Posts
    2,666
    According to the boiler manual the boilers circulator for the Ultra -80 and -105 takes a Taco 007. The Ultra -155, -230, and -310 take a Taco 0011.

  7. #20
    Join Date
    Mar 2002
    Location
    Gaylord, Michigan
    Posts
    729
    Originally posted by beenthere
    Some thing may have gotten into it, or it may be a defective unit.
    Its under warranty, have it replaced if defective, or the obstrution removed.



    Chris:
    The Ultra 230 requires a 0011 for the primary loop.

    Wow, okay thanks for the heads up!

  8. #21
    Join Date
    Sep 2005
    Posts
    73
    I opened the 011 twice already and cleaned it out and so forth. I think it just might be bad and needs to be replaced.

  9. #22
    Join Date
    Feb 2004
    Location
    michigan
    Posts
    677

    Wink

    I'm thinking the 0011 pump might be a problem. That does have a high curve to it as far as head. I'v been using the 007 pump for short primarys because they don't usually have any head to speak of. I have had problems with the 0011 in the past due to manufactor reconmendation which maybe wasn't the best way to go. Check the size and make sure 0011 is the right pump for your application.
    FYI I have hot water baseboard at home and I can hear a chine (ring) in some rooms but I'm just too lazy to fix it. Go figure, the cobbler has no shoes.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event