Kind of Urgent, Carrier 38apd and bleed port txv's
Is it a big deal ordering a valve with a bleed port?
Set new units yesterday{condensor and a sterling mua unit with a dual circuit evaporator) and no expansion valves were shipped.
Carrier tells me its 2-3 weeks for the valves.
Service instruction state 5-15% bleed port valves required.
Sporlan tev selection literature vauge on this subject.
Anyone ever pick these up before? I understand what they are and why I need them. Just need them fast.
ThanksIf you cant fix it right, try again.
-
10-26-2010, 09:38 PM #2
Professional Member*
- Join Date
- Dec 2005
- Posts
- 1,655
If it is R-22, then use any sporlan valve with CP100.
Ex: TEV-8-CP100
-