    Kind of Urgent, Carrier 38apd and bleed port txv's
    Is it a big deal ordering a valve with a bleed port?
    Set new units yesterday{condensor and a sterling mua unit with a dual circuit evaporator) and no expansion valves were shipped.
    Carrier tells me its 2-3 weeks for the valves.
    Service instruction state 5-15% bleed port valves required.
    Sporlan tev selection literature vauge on this subject.
    Anyone ever pick these up before? I understand what they are and why I need them. Just need them fast.
    Thanks
    If you cant fix it right, try again.
    If it is R-22, then use any sporlan valve with CP100.
    Ex: TEV-8-CP100
    Jun 2001
    Northwest Indiana
    Quote Originally Posted by just_opinion View Post
    Ex: TEV-8-CP100
    Its 410A
    Dallas ,Texas
    APD's are so new I'm not surprised that supply hasn't caught up with demand.
    UA 100
    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
    Quote Originally Posted by toptech View Post
    Its 410A
    Then get any 410A TXV. If you don't want it to bleed, then LLSV. Want it fast right.
    Dallas ,Texas
    Its 410A
    As long as you get the charge within 2 lbs you should be good.