Results 1 to 8 of 8
    Oct 2010
    York warning help
    I have a York chiller with a warning eroor on the screen-
    CONDENSER OR
    EVAPORATOR
    XDER ERROR-
    Chiller info.
    YORK CHILLER
    MODEL# YTGOAIB-CGJ
    SERIAL# 035-16287000
    What is this warning? No specifics listed that I can find?
    Jun 2010
    U.A. (upper Alabama)
    Are you sure that's exactly what it says?
    Dec 2009
    Southern US
    Haven't seen that error before but thats probably not suprising!
    I think you will find your listed S# is the part# for your control cabinet!
    Some of the Yorkies here may have seen your problem before.
    I'm good at making things cold...You can ask my first two wives!
    Jun 2010
    Check your press. transducers with chiller off if possible to see if one is reading out of wack. If not possible, check them with a gauge. I have seen evap. press. transducer or probe error but this warning is usually noncondensibles, making the approach negative.
    Oct 2010
    yes
    Yes, exactly what is says.
    Dec 2008
    Dixiana, AL
    Are you sure it's not reading something like "Evaporator transducer or probe error"?
    Western Wa
    Noncondensibles, most likely.
    God Bless our Veterans
    God Bless the USA
    Central Oregon
    I'm with RandyS, you've got air!
    When the going gets weird, the weird turn pro. HST