Thread: harvest problem
-
12-14-2004, 09:57 PM #1
Professional Member
- Join Date
- Dec 2000
- Location
- oklahoma
- Posts
- 85
Working on manitowoc B 250 water cooled ice machince. Makes ice in freeze cycle,goes into defrost but ice does not drop.Put level on machine and tilted to front just little. Ice pattern looks good, hot gas valve is opening at least a litte because line at bottom of evap.plate is warming up. Can a dirty evaporator plate cause this problem ? Although it looks ok. Or can the hot gas valve not open all the way ? Can I check valve by measuring temp on both sides of valve ? Didn't have much time today to really check out going back tomarrow morning.
-
12-14-2004, 10:27 PM #2
Regular Guest
- Join Date
- Jan 2004
- Posts
- 27
need more info. does ice melt away? is ice thickness correct? does ice continue to build up? explain what is happening.
-
12-14-2004, 10:42 PM #3
Professional Member
- Join Date
- Dec 2000
- Location
- oklahoma
- Posts
- 85
It will try to go into harvest. But ice will not come off evaporator plate. After being in defrost for 3 minutes it will finally kick back into freeze cycle. Ice thickness probes will then send it back ito defrost mode. It will do this 3 times before it goes into lockout and give code of 3 harvests over 3 minutes. Sometimes I am told the ice will drop on the second try of defrost. Ice thickness is good and probes are working or it would not go into defrost.
[Edited by jgjn on 12-14-2004 at 10:45 PM]
-
12-14-2004, 11:06 PM #4
Regular Guest
- Join Date
- Jan 2004
- Posts
- 27
clean evap with proper chemical. sounds like eveap coil dirty.
-
12-14-2004, 11:19 PM #5
Professional Member
- Join Date
- Aug 2002
- Posts
- 6,047
Do what the guy above me said.
Plus replace the thickness probe. Cheap insurance. Make sure you adjust the probe correctly.
Also, get in there real close and inspect the plate to make sure no one has used to hammer and screwdriver to "assist" the harvest.
Little nicks in the surface of the plate show vandelism. Bad news.
There is other stuff to look out for also.
While your at the deal buying that probe, get the small book on the machine. AND some nickel safe ice machine cleaner.
Your on the right track though.
-
12-14-2004, 11:52 PM #6
First of all you need a book.
You can not tell if the plate is limed up if its wet. clean it first like skoch and R12 said.
Making the ice is the easy part. Harvesting the ice is more critical in my eyes.
You actually have to generate enough heat for harvest, the discharge line must reach 160 deg. before harvest or you dont have enough heat to drop the ice.
If you dont reach 160 then you might have problem with superheat.(txv bulb loose or not insulated)
You need a book because it could be anything.
Dont install your long hvac gauges. Dont install any unless you know for sure its a refrigeration problem. If you already have then now you are low on freon.
you need more freon to harvest ice than to frezze it. Slighty low could cause longer harvest.
-
12-15-2004, 12:20 AM #7
Professional Member
- Join Date
- Dec 2003
- Location
- Location!, Location!
- Posts
- 929
Check the weep holes in the back of the plate-should be clear. Use a nickel-safe delimer to clean plate -Calgon has one. How old is this machine? Manitowoc had some problems with warping a while back, and the make a cube gauge to check the individual cells. Also if there is any missing nickel plating, that also will grab. Can you pull the ice plate away from the evaporator? What is the bridge thickness when you try for the first harvest?-should be 3/16". What is the refrigerant and the head pressure? What is the condenser water outlet temp? The bridge sensor is probably fine- if the bridge is not too thick, that problem is usually a short(always harvesting) or an open(never harvesting).
-
12-15-2004, 09:10 AM #8
Professional Member
- Join Date
- Jul 2003
- Location
- Upstate SC
- Posts
- 384
also make sure your cond fan is shutting off in the defrost mode, b models are famous for the SCR delay timer to short and backfeed voltage to fan!!
-
12-15-2004, 06:18 PM #9
Regular Guest
- Join Date
- Jan 2004
- Posts
- 27
you defenitly are getting expert help from the other guys. don't forget to time the defrost cycle. had one where the time was way short- turned out to be a bad circuit board.
-
12-15-2004, 06:29 PM #10
Clean the evaporator with a good nickel-safe acid cleaner. If the evaporator surface isn't shiny clean like nickel should be, isn't slick and smooth like it should be your evaporator and therefore your machine is toast. Don't waste your time.
It's a B-Series. It has to be ten years old or so. It's lived its life. Let it go.
-
12-15-2004, 07:45 PM #11
Professional Member
- Join Date
- Dec 2004
- Location
- Louisville, KY
- Posts
- 6
I think the key to this problem is the water regulating valve. Is it shutting off tight during the defrost or is there a small trikle of water thru the condenser causing the head pressure to be too low and losing the needed heat for a proper defrost. Check the water regulating valve I bet it is leaking thru.
-
12-15-2004, 11:38 PM #12
Professional Member
- Join Date
- Dec 2004
- Posts
- 18
look behind plate for seperation of tubing, or check seals on sides if it has them and if not make sure you are not forming ice through the sides and holding the plate.
-
12-16-2004, 05:01 PM #13
Professional Member
- Join Date
- Dec 2000
- Location
- oklahoma
- Posts
- 85
Thanks for all the reply's. I have the book on the manitowoc machines. But with all the years of accumulated knowledge on this site I just posted thread. And I wasn't disappointed. It was the water regulating valve. Didn't have enough head pressure to properly harvest ice. Thanks again for the help.