Results 1 to 13 of 13
    Oct 2010
    VAV Box (Cooling Min. CFM)
    Hello
    I'm getting mixed answers about what value the Minimun value CFM should be
    on a VAV box with Reheat.
    Is it 30-50% of the design cfm (Max. CFM)? 300cfm? or untill there's enough air for ventilation?
    I hope that's enough information.
    Mar 2009
    Triad - North Carolina
    The installation manual will detail those settings and parameters
    Yes, I've seen that before and it doesn't mean I like it.
    Sep 2010
    NY
    I think it depends on the box size, static pressure and damper position. (vav) I think that is what is going to dictate the cfm flowing through the vav box. There might be a chart which intersects cfm with static for the box size. I will interested to see what others post.
    Oct 2010
    Austin, TX
    Its also going to depend on the reheat set up and how big it is.
    Is it electric reheat or hot water? Does it have a fan?
    If you're too "open" minded, your brains will fall out.
    Artificial intelligence is no match for natural stupidity.
    Jun 2010
    Philadelphia PA
    The min is a design concern not a system requirement meaning under the old rules for fresh air, you needed to make sure you had X CFMs per person delivered to the space. Now that we are monitoring CO2 some of that may have gone away. You may need to look at the drawings, original design intent before you take it upon yourself to "deny the occupants a healthy space" If that sounds like what a lawyers complaint might sound like, well it is!
    Also whoever asked about electric reheat also understands you need min airflow so the elec coils/elements don't burn up is also right on
    Stafford, Va. USA
    Hi Shrend,
    You are correct, this setting should be used for minimum outside air ventilation, when the cooling requirement is satisfied.
    In the days of inlet guide vanes (IGV), this setting would be higher because the IGV could only throttle the the supply air flow down to 30% of the total supply air flow from the supply fan.
    With the use of variable frequency drives (VFD), the cooling minimum can now be set much lower. This provides additional benefits, better comfort for the occupants and more energy saving because the supply fan can be run at lower speeds for lower air flows.
    Allen
    UA Local 602
    A man who says that he can't learn anything in a class is exactly right.
    occupancy type is also a consideration. in medical suites for example requirements are higher in some cases.
    Oct 2010
    Austin, TX
    Gracia Genduct.
    Oct 2010
    Thanks guys.
    Thanks for all the information
    Oct 2010
    Most VAV's are set at @ 10% as a rule of thumb if you don't have access to design spec's.
    Quote Originally Posted by shrend View Post
    Hello
    If Reheat is electric and VAV is cooling only, then 70 CFM per KW is typical. Some people use 100 CFM per KW to be safe. Most velocity sensors are accurate down to .03" of velocity pressure, fall below that and you will have problems with control system measuring the flow. Hope this helps.
    Oct 2010
    Austin, TX
    Hey someone answer this one it has me kinda boggled. I have a VAV box with a 3 stage electric reheat. I have a normal sized classroom of 14x17x12. No equipment(computers, projectors, so on). I have 6 tables with 4 chairs a table. So I am looking at 30ish people in the room. It has a I/A series DDC with a minimum CFM of 1330?!? At first I thought well maybe there is a CO2 hidden somewhere but nope. The AHU blows 1.2 WC and 55 degrees 24/7.
    I showed up because the room was cold at 60 degrees with a setpoint of 76 degrees. Turns out after a few hours of testing it was a .5 WC pressure safety switch for the reheats mounted upside down(according the manufacture specs) and a clogged Hi pneumatic line.
    But I still can't figure out why you would have a 1330 CFM on a room that size with that many people. I could understand if it was a 25x25x12 with 40+ people.
    Hampton Roads, Virginia
    Quote Originally Posted by XcelTech View Post
    A classroom should have 15CFM of outside air per occupant, 30*15 = 450 CFM, but what % of the delivered air is outside air ? Lets say its 25% then you would need to deliver 1800 CFM of air.
    Ideally classrooms should have a DOAS delivering 68Ί 50%RH air at 15 CFM/Occupant, and then use the main system to meet the cooling/heating needs only.
    Kevin
    "There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria
    "It's not the customer's job to know what they want." -- Steve Jobs