    Lochinvar Power Fin

    Hey guys,
    I have a Power Fin M#IBN1500 S#G08H0021048. I am doing the start up on this unit. We have been brought in after the installing contractor had an issue with it (Heat exchanger was twisted and pissing water).

    The start up looks good. The bypass is maintaining a 136 degree temp.
    My only concern is that the IOM states they are looking for a 3.5" w.c. pressure difference for both air and gas pressure. I have a 4.1" w.c. both for gas and air. I have the 1 to 1 ratio they are looking for but I can't get the pressure any lower even by moving the tube for the low side of the air tube on the burner.

    thoughts?

  2. #2
    Join Date
    Mar 2009
    Location
    VB
    Posts
    322
    Are you using a water or a gauge man"o"meter?????
    If I would of killed my wife when I first met her, I'd be out of jail by now!

    GET SOME!!

  3. #3
    Join Date
    Apr 2007
    Location
    Pa
    Posts
    758
    Verticle u tube

  4. #4
    Join Date
    Apr 2007
    Location
    Pa
    Posts
    758
    talked to lochinvar and they said that doesnt concern them. If it would have been higher than 4.5 they would be concerned