Results 1 to 7 of 7
    Lenexa, KS
    Question
    I am looking for a formula to calculate both the Heat of Extraction (HE) and Heat of Rejection (HR) for Ground Source Heat Pumps.
    I have the following variables to plug into the formula:
    Return Air temp
    Supply Air temp
    CFMs
    EWT
    LWT
    GPMs
    The unit is in the HEATING mode.
    If you can help me out I would greatly appreciate it!
    "We are what we repeatedly do.
    Excellence, then, is not an act, but a habit."
    -Aristotle
    Nov 2000
    Manhattan, Kansas USA
    Heat of Extraction/Rejection formaula is:
    HE or HR = Delta T (water) x GPM x brine factor.
    pure water brine factor is 500
    anti-freeze is 485
    From what you have listed, you will still need to know if it is pure water, or a mix to get your brine factor.
    swany
    Nov 2001
    east kansas
    Isn't there another formula to figure the gallons per minute involving Delta P (pressure)
    Lenexa, KS
    Thanks swanny!
    -Aristotle
    Apr 2002
    There would be Lynn, but every water to refrigerant heat exchanger would have a different flow vs pressure drop relationship.
    For a particular unit there could be a published table or a chart to get the flow from once you measured the pressure drop.
    http://www.ductstrap.com/
    Nov 2001
    east kansas
    So you can't figure HE/HR without figuring GPM first. And you have to have the manufacture's published data.
    Apr 2002
    Yes you need to know the flow. You can install a flow meter and read direct or take pressure readings and use the manufactuers data. You could make a formula for each type of heat exchanger to use the pressure readings without looking at a table or a chart.