Good luck with that. It's not even on the Trane site.
-
10-20-2010, 07:07 AM #3
yea ., this is the thing., ihave the rtaa iom which everyone has, and i have the diag troubleshoot and repair manual also i have the rtaa chhb compressor troubleshooting ., with all this info you would think that this would b enough, guess not, all of these manuals have great info and troubleshooting procedures, WOW CAN SB5 B THAT IMPORTANT., ., must be lots of trane secrets in there.,??idk
but i know of a great friend that will help,,ed me ,,,thanks boss manno signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
10-20-2010, 04:03 PM #4
Control Operation, Setup and Troubleshooting for RTAA Series R Air-Cooled Chiller Control Panel. UCM
That is the title of the lit. It was published in 6-1-1992.
I am curious why you have need of it if you were unsure what it pertained to.
-
10-20-2010, 11:02 PM #5
i know what it is and what it is pertaining to., just when i am reading and following up with some of the other lit tells me to refer to it., so i would go there and venture but.....
had a bud give it to me though
thanksno signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
10-21-2010, 06:46 AM #6
Regular Guest
- Join Date
- Feb 2010
- Posts
- 81
I got it , whats the go though, you seem to ask for a lot of service bulletins , manuals etc reading won,t teach you everything
-
10-21-2010, 05:01 PM #7
Professional Member
- Join Date
- Nov 2006
- Location
- North Carolina
- Posts
- 125
Here you go, dont tear anything up.
-
10-21-2010, 06:16 PM #8
nope ., u r exactly right., but theory and field go hand in hand., also, i still have alot to learn., thanks rover and chad.,
soon, instead of asking i will be helping othersno signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
10-21-2010, 08:19 PM #9
-
10-23-2010, 06:51 AM #10
Regular Guest
- Join Date
- Feb 2010
- Posts
- 81
Majority of calls to these chillers I have found are due to oil problems but are not oil related as such , head pressure control to these chillers is essential, if you have failed fans etc you will have dramas.
There are upgrades available for more aggressive fan staging if your ambient requires. Also uprades for exv's .
Exv upgrade provides valves with site glass to view valve position similar to what you will see on a rthd .
-
10-23-2010, 12:23 PM #11
Upgrades
The only problem with Trane's EXV upgrade package is you will have to change out all of the electronic expansion valves could be 2-4 valves depending on machine size and all the exv board(s). This is quite expensive if your only trying to gain control of head pressure at start up and don't have any exv issues. I had an RTAA 340 in a lab that was 100% outside air and after any shut down during the summer 95+ degrees with 99% humidity even the new chip for fan control wouldn't help. I just slowed down the chilled water reaction timer setting, problem solved.-GEO
Of all the things I have lost in my life, I miss my mind the most-GEO
-
10-24-2010, 03:33 AM #12
Regular Guest
- Join Date
- Feb 2010
- Posts
- 81
-
10-24-2010, 02:03 PM #13
Options, Opinions, Out to lunch
Rover, no of course not. It is just in my case thats what worked for me. It is actually funny as Trane was out at this plant doing the start-up and their tech was "lost in space" because of this problem, His supervisor came out and it was more like Homer Simpson and the trailer park quartet trying to figure this one out. Their actual solution was to tie all of the fan contactor coils together at start-up and even that didn't work, when you have 96*F entering water.-GEO
Of all the things I have lost in my life, I miss my mind the most-GEO