  1. #1

    Run Capacitor Question

    Air conditioner not working, circuit board and run capacitor are out. Called AC Company and the price for installing circuit board was unreasonable and customer service was unsatisfatory. Company said they could get unit working by replacing capacitor and routing around circuit board straight to fan motor but fan motor would run 24/7. I told them I was ok with that and repairs were made.

    1 1/2 months went by and both units and everything in attic went out, breaker continued to reset. Called electrician and diagnosed as a ground in ac unit that was previously worked on. Called new AC company and was told that a 12.5 msd capacitor was installed instead of a 10.0, burned up my fan motor and the ground caused the electrical problems. New AC company installed new Capacitor, circuit board and fan motor.

    Called old company to tell them about installing incorrect capacitor, was told that I was wrong, sent them proof and was told it was not their error as the wrong size capacitor had nothing to do with fan burning up instead it was the fan running 24/7 that did it.

    New company said circuit board had nothing to do with fan motor going out and that if anything it helped the life of the fan motor as there was no stopping or starting of the fan motor for 1.5 months.

    I am confused......what is the correct answer?

  2. #2
    Not sure exactly what is going on there but you can change a 10mfd run cap with a 12.5 one, there is a margin of error you can use and I think thats close enough.
    Is this a heat pump?
    Hey cockroach, don't bug me!

    www.AskTheDiceman.com

    www.TheColdConspiracy.com

    www.Pennwood-HVAC.Com

    Bring Em Home....

  3. #3
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    2,696
    The correct answer is you should have had it fixed RIGHT in the FIRST PLACE and not be here trying to figure out if CASCADING problems caused you issue.

    Sorry if this is a rant, but I HATE going to jobs that some cheapscate has cobbled together "to get it running" and never returns to FIX IT CORRECTLY!
    It's not the Brand with the fewest repairs-It's all in the install!!! Attention to detail and using the best materials!

  4. #4
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    14,437
    The capacitor didn't cause the problem. The motor probably just gave it up, and when it burnt up it likely caused the ground.

    The first service company was unwise to rig it. You were also unwise by not taking their first suggestion of fixing it right. The first "repair" might not have had anything to do with the motor failing; but if so, you're as responsible as they are.

    Lick your wounds and learn from it. Always use a pro, and always fix it right.

  5. #5
    Quote Originally Posted by k_fridge View Post
    The capacitor didn't cause the problem. The motor probably just gave it up, and when it burnt up it likely caused the ground.

    The first service company was unwise to rig it. You were also unwise by not taking their first suggestion of fixing it right. The first "repair" might not have had anything to do with the motor failing; but if so, you're as responsible as they are.

    Lick your wounds and learn from it. Always use a pro, and always fix it right.
    Thank you very much, that is exactly what I needed to hear.

    Lesson Learned and thank you for your honest opinion and willingness to help.

  6. #6
    Join Date
    Sep 2010
    Location
    Lufkin, Texas
    Posts
    22
    It still amazes me that people will agree to a service company doing a half ass repair as a way to get them buy because they don't have the money to fix right, knowing that something like that will not last, and then get pissed with the service company when it does not last.

    edit... after seeing your last post I'm glad to see you accepting the truth and not being all but-hurt about it like most.

  7. #7
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,020
    Quote Originally Posted by Ryan C View Post
    Air conditioner not working, circuit board and run capacitor are out. Called AC Company and the price for installing circuit board was unreasonable and customer service was unsatisfatory. Company said they could get unit working by replacing capacitor and routing around circuit board straight to fan motor but fan motor would run 24/7. I told them I was ok with that and repairs were made.

    1 1/2 months went by and both units and everything in attic went out, breaker continued to reset. Called electrician and diagnosed as a ground in ac unit that was previously worked on. Called new AC company and was told that a 12.5 msd capacitor was installed instead of a 10.0, burned up my fan motor and the ground caused the electrical problems. New AC company installed new Capacitor, circuit board and fan motor.

    Called old company to tell them about installing incorrect capacitor, was told that I was wrong, sent them proof and was told it was not their error as the wrong size capacitor had nothing to do with fan burning up instead it was the fan running 24/7 that did it.

    New company said circuit board had nothing to do with fan motor going out and that if anything it helped the life of the fan motor as there was no stopping or starting of the fan motor for 1.5 months.

    I am confused......what is the correct answer?
    Are you able to sift through all this? Let's review.

    The capacitor was not a fundamental issue. Motors are very tolerant of a 10% difference in rating. You had an old motor.

    Never ask for a partial repair. Always get the right repair.

    Always use the right company. They won't do a half-a**ed repair.

    Find the right company:

    ask several friends which company they have used that did a satisfactory repair. Long standing relationships in that knowledge pool is best, by far. Use one of the recommended contractors, and say "(insert friend's name here) told me you do a great job."

    Have that company make the right, permanent repair, with a warranty of some sort.

    Shorts to ground are common problems in failing electrical components. This does not represent poor workmanship or a bad manufacturer. It is simply a failure. They happen.

    Questions?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  8. #8
    Join Date
    Apr 2010
    Location
    East of Lyndon's
    Posts
    525
    Probably nothing wrong with using the capacitor temporarily until you can get the right one but I wouldn't advise leaving it in. I don't believe it's easier on a condensing fan motor to let it run 24/7 than to let it start and stop with the unit. The fan motors don't use start switches. I agree you should have fixed it right the first time!!
    If you can't fix it with a hammer, you've got an electrical problem.

  9. #9
    Join Date
    Oct 2010
    Location
    STL
    Posts
    387
    Quote Originally Posted by beshvac View Post
    The correct answer is you should have had it fixed RIGHT in the FIRST PLACE and not be here trying to figure out if CASCADING problems caused you issue.

    Sorry if this is a rant, but I HATE going to jobs that some cheapscate has cobbled together "to get it running" and never returns to FIX IT CORRECTLY!
    What, I love when that happens, then we get to charge more because the number of other things that went wrong because the costumer wanted to be cheap.

  10. #10
    Join Date
    Dec 2001
    Location
    Ocean Pines, MD
    Posts
    6,935

    I love it when this happens.

    Quote Originally Posted by Ryan C View Post
    Thank you very much, that is exactly what I needed to hear.

    Lesson Learned and thank you for your honest opinion and willingness to help.
    Someone listened, learned and said thanks.

    Ripping them more afterwards??????

  11. #11
    Join Date
    Dec 2005
    Posts
    3,822
    I'm amazed how many think 12.5 instead of 10 is within 10%.

    Oh though I dont' think that would necessarily cause a problem. Leaving the motor to just run is not something I would want do for more than a day and only if I had no better option at the time and I explained the risks to the customer. And I wouldn't leave that capacitor in long term either. Its hard to say for sure what caused the problem but you leave yourself open to alot of criticism when you do obvious wrong things.

  12. #12
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,020
    Quote Originally Posted by newoldtech View Post
    I'm amazed how many think 12.5 instead of 10 is within 10%.
    10% of 10 is one. That makes 11 uf on the upper end.

    Then, you can consider that the capacitor is built to a tolerance that is 5 to 10%. A capacitor that says 12.5 on the side may be closer to 11.8 uf.

    So, while not exactly a 10% difference between to two caps, you can feel comfortable that using a 12.5 in place of a 10 will get the job done until a more precise cap can be obtained and installed. It is unlikely that using a 12.5 in place of a 10 is going to cause an imminent failure of a motor.

    So, to review: motors easily tolerate a 10% difference in the cap value, and they will tolerate more of a difference from the ideal value when pressed.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  13. #13
    Join Date
    Dec 2005
    Posts
    3,822
    Quote Originally Posted by timebuilder View Post
    10% of 10 is one. That makes 11 uf on the upper end.

    Then, you can consider that the capacitor is built to a tolerance that is 5 to 10%. A capacitor that says 12.5 on the side may be closer to 11.8 uf.

    So, while not exactly a 10% difference between to two caps, you can feel comfortable that using a 12.5 in place of a 10 will get the job done until a more precise cap can be obtained and installed. It is unlikely that using a 12.5 in place of a 10 is going to cause an imminent failure of a motor.

    So, to review: motors easily tolerate a 10% difference in the cap value, and they will tolerate more of a difference from the ideal value when pressed.
    I disagree. To me 10% means 10%.

    Especially with the capacitors we've all been dealing with lately. They don't seem to have any "tolerance" even when you use the right size one. So in a fix I might use a 12.5 instead of a 10 but I would go back to change it.

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event