Thread: question??

  1. #1
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    992

    Cool question??

    if doing an annual , machine is running fine and water temp is good., but we want to run the machine 100% for 30 min to see what happens ., or may be try to move some oil around., how is the machine going to allow this to happen ??

  2. #2
    Join Date
    May 2008
    Location
    Central Pennsylvania
    Posts
    435
    That can be tricky at times. You'll have to put a load on the machine one way or another. Either by running the setpoint down a few degrees or shutting the chiller down for a few minutes and restarting it if possible. Pretty much depends on the demands of the building as to what you can do.

  3. #3
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,817
    i always do them first thing in the morning before they come on, usually the mechanical ciilong comes on at 7 or whatever
    for example this morning working at the mall, it usually comes on at 9 oclock
    he let the mall warm up until about 10 or so.
    the return water will be 75 degrees and the machine will load up nice...
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  4. #4
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    992
    Quote Originally Posted by supertek65 View Post
    i always do them first thing in the morning before they come on, usually the mechanical ciilong comes on at 7 or whatever
    for example this morning working at the mall, it usually comes on at 9 oclock
    he let the mall warm up until about 10 or so.
    the return water will be 75 degrees and the machine will load up nice...
    one more thing, if running @ 100% , does that help bring oil back or is it the other way around.,running say 40%??

  5. #5
    Join Date
    May 2008
    Location
    Central Pennsylvania
    Posts
    435
    Quote Originally Posted by mlkwal1 View Post
    one more thing, if running @ 100% , does that help bring oil back or is it the other way around.,running say 40%??
    Better oil return with chiller running loaded.

  6. #6
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    788
    If you have preheat coils on the AHU's you can run the setpoint up to 90 deg. or so to give you a false load.

  7. #7
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    788
    Quote Originally Posted by mlkwal1 View Post
    one more thing, if running @ 100% , does that help bring oil back or is it the other way around.,running say 40%??
    Depends on the chiller.