Quote Originally Posted by supertek65 View Post
yeah
rthd is also falling film 2 eexv's

if you run cold condenser water even for a short tim
you will be pumping refrigerant back up from the bottom of the evaporator!!!!!!!!!!!!
using your shiny little g5 twin
Smaller tonnage machines have only one eev. I havent seen what your second sentence is talking about. How can this happen. Typically cold condensor water would be handled by a condensor water regulating valve controlled by the CH530. Why would it stack ref. in the evap.