  1. #14
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,609
    Perk's correct about why you saw what you did on the display. What was the very first thing that came up on the history buffer, before you started scrolling?

  2. #15
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,423
    Quote Originally Posted by klove View Post
    Perk's correct about why you saw what you did on the display. What was the very first thing that came up on the history buffer, before you started scrolling?
    Errrrrrrrrr...................I forgot?

    Bad answer, I know
    Pretty sure, but not positive, that was the message. (which was SYS 2 WYE DELTA ON)
    \m/
    original member of the racoon brotherhood

  3. #16
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,609
    You can scroll either direction once you get into the history buffer. If you go in reverse order, I believe the first thing you see is the last item in the operating data at the moment of shutdown. If you hit "history" and whichever buffer you want to go into (should be 1-6), and then "enter", the fault for that shutdown will come up. Then scroll through using the up/down arrows. If you don't see general unit info like outdoor temp and time of shutdown, etc, you're heading the wrong direction.

  4. #17
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,423
    Thank you, Klove.
    Before cperk's reply, I was 100 % sure in the history, faults 1&3 were "wye delta on"
    Now I'm 95%.
    Ddn't see an outdoor temp (that I remember), but did see time.
    \m/
    original member of the racoon brotherhood

  5. #18
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    832
    Quote Originally Posted by heavymetaldad View Post
    Thank you, Klove.
    Before cperk's reply, I was 100 % sure in the history, faults 1&3 were "wye delta on"
    Now I'm 95%.
    Ddn't see an outdoor temp (that I remember), but did see time.
    Wye delta on means both the wye and the delta contactor were pulled in (running full speed after transition). I think that if the chiller was seeing the delta contactor pulled in, or a stuck auxillary at or before startup, it would have to be repaired before it would reset. I don't think the chiller would let it startup on a non-latching fault if this happened.
    Last edited by cperk; 10-07-2010 at 09:43 PM. Reason: more info

  6. #19
    Join Date
    Dec 2009
    Location
    Fort Worth, Texas
    Posts
    151
    The codes in the history have to be cleared. The unit was reset but the history is still showing the faults.

  7. #20
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,423
    I may be going back there later this week.
    Thanks guys for your replies.
    \m/
    original member of the racoon brotherhood

  8. #21
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    832
    Hey dad, I went and looked at one today, if you hit history, then the number of the fault 1-6 (6 being the last fault) then enter, the first thing to come up is the date and time of shutdown, then if you scroll down, (with arrow) the first thing you see is sys. 2 wye delta on or off, according if system 2 was running at the time of the fault,even if cir. 1 generated the fault, but if you hit the up arrow it shows cir. 1 fault whatever or no faults and cir. 2 fault whatever or no faults on the same screen.

  9. #22
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,423
    Thanks cperk. Learn something new every day. I haven't been back, and it looks like the job (if there is one) is being pushed back to spring.
    \m/
    original member of the racoon brotherhood

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event