    Another YCAS thread

    YCAS0208EB17
    Anyone be kind enough to forward or post the IOM? Just spent alot of time going thru 76 threads of YCAS topic, and not 1 IOM. I'd like to read up on this unit, saw on Friday in the faults '2 Wye Delta ON'. Both compressor were running. Was told by building engineer unit did not need reset (?)
    Thanks, bOb.
    \m/
    original member of the racoon brotherhood

  2. #2
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,595
    Here you go dude.
    Attached Files Attached Files
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  3. #3
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,426
    Thank you.
    \m/
    original member of the racoon brotherhood

  4. #4
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,426
    Quote Originally Posted by heavymetaldad View Post
    YCAS0208EB17
    Saw on Friday in the faults twice was '2 Wye Delta ON'. Both compressors were running. Was told by building engineer unit did not need resetting (?)
    Thanks, bOb.
    Well, that fault is not in the book. I would think that an aux. contact was made that should have been open when compressor was off.
    Any input / ideas?
    \m/
    original member of the racoon brotherhood

  5. #5
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    837
    Quote Originally Posted by heavymetaldad View Post
    Well, that fault is not in the book. I would think that an aux. contact was made that should have been open when compressor was off.
    Any input / ideas?
    If your in the fault history, you might have scrolled the wrong way. It shows everything the circuit is doing at the time of the fault, ie. wye delta on, llsv open, fan stage whatever, and so on. Hope this helps. Could have been just a power failure and the first thing that shows up in the history if scrolling the wrong way is sys 2 wye delta on.

  6. #6
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,595
    There are three contactors 1 small 2 large can't remember for sure but check small contactor to see if there is interlock contact because on start thats engaged then drops on transition and both large are engaged and I believe that one of those has a interlock contact also possible that small one is still engaged once that contactor drops out , haven't seen this fault.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  7. #7
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,426
    Quote Originally Posted by cperk View Post
    If your in the fault history, you might have scrolled the wrong way. It shows everything the circuit is doing at the time of the fault, ie. wye delta on, llsv open, fan stage whatever, and so on. Hope this helps. Could have been just a power failure and the first thing that shows up in the history if scrolling the wrong way is sys 2 wye delta on.
    First time I've seen this version of millenium. Don't believe I scrolled it incorrectly, but I may be wrong. Thanks for the input.
    \m/
    original member of the racoon brotherhood

  8. #8
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,426
    Quote Originally Posted by york56 View Post
    There are three contactors 1 small 2 large can't remember for sure but check small contactor to see if there is interlock contact because on start thats engaged then drops on transition and both large are engaged and I believe that one of those has a interlock contact also possible that small one is still engaged once that contactor drops out , haven't seen this fault.
    I won't be heading back there soon, but I will keep it in mind.
    Interesting you haven't seen this fault - but it was in the stored history, twice, although bldg. engineer stated that the machine was not reset. (could be not the complete truth)
    Thanks for the input,
    \m/
    original member of the racoon brotherhood

  9. #9
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,595
    Just looking thru the service book what may have happened is this micro calls for compressors to start turns on relay outputs (wye delta on ) compressors attempt to start but no 3 phase is on times out then faults micro logs fault then power is restored machine then restarts micro is most likely auto restart chiller back on line and running just a guess but makes sense look at page 20 in this IOM it explains the start sequence very well that interlock that I was talking about is not what I thought it was its for interlocking the contactors together.
    Attached Files Attached Files
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  10. #10
    Join Date
    Dec 2006
    Location
    Somewhere in Canada
    Posts
    84
    Our THANKS to YORK56, your thoughfulness in posting the IOM is greatly appreciated. We take this opportunity to express our Thanks.

  11. #11
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,426
    That is a great explanation.
    Thanks again for the pdf, and the insight
    \m/
    original member of the racoon brotherhood

  12. #12
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,595
    Some machines have single point power some don't the ones that don't the 120 volt control circut would be energized even when the 3 phase isn't which would give you this condition.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  13. #13
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,426
    Not sure how it's configured, although loss of 3 phase power would have rung some bells and blew whistles.
    \m/
    original member of the racoon brotherhood

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event