Another YCAS thread
YCAS0208EB17
Anyone be kind enough to forward or post the IOM? Just spent alot of time going thru 76 threads of YCAS topic, and not 1 IOM. I'd like to read up on this unit, saw on Friday in the faults '2 Wye Delta ON'. Both compressor were running. Was told by building engineer unit did not need reset (?)
Thanks, bOb.\m/
-
10-03-2010, 06:43 PM #2
Here you go dude.
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
10-03-2010, 06:50 PM #3
Thank you.
\m/
-
10-04-2010, 06:50 PM #4
-
10-04-2010, 08:21 PM #5
If your in the fault history, you might have scrolled the wrong way. It shows everything the circuit is doing at the time of the fault, ie. wye delta on, llsv open, fan stage whatever, and so on. Hope this helps. Could have been just a power failure and the first thing that shows up in the history if scrolling the wrong way is sys 2 wye delta on.
-
10-04-2010, 08:41 PM #6
There are three contactors 1 small 2 large can't remember for sure but check small contactor to see if there is interlock contact because on start thats engaged then drops on transition and both large are engaged and I believe that one of those has a interlock contact also possible that small one is still engaged once that contactor drops out , haven't seen this fault.
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
10-05-2010, 05:55 PM #7
-
10-05-2010, 05:58 PM #8
-
10-05-2010, 07:02 PM #9
Just looking thru the service book what may have happened is this micro calls for compressors to start turns on relay outputs (wye delta on ) compressors attempt to start but no 3 phase is on times out then faults micro logs fault then power is restored machine then restarts micro is most likely auto restart chiller back on line and running just a guess but makes sense look at page 20 in this IOM it explains the start sequence very well that interlock that I was talking about is not what I thought it was its for interlocking the contactors together.
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
10-05-2010, 07:15 PM #10
Professional Member
- Join Date
- Dec 2006
- Location
- Somewhere in Canada
- Posts
- 80
Our THANKS to YORK56, your thoughfulness in posting the IOM is greatly appreciated. We take this opportunity to express our Thanks.
-
10-05-2010, 08:04 PM #11
That is a great explanation.
Thanks again for the pdf, and the insight\m/
-
10-05-2010, 08:41 PM #12
Some machines have single point power some don't the ones that don't the 120 volt control circut would be energized even when the 3 phase isn't which would give you this condition.
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
10-05-2010, 08:57 PM #13
Not sure how it's configured, although loss of 3 phase power would have rung some bells and blew whistles.
\m/