    Best Practices

    I'll keep it brief.

    My Situation: offer support and guidance to other techs.

    My Question: Your oppinion on the actuall use of nitrogen and micron gauges in the field. What percentage of techs actually do as they are instructed.

    It can be obvious at times during follow-ups what was not done or done wrong.

  2. #2
    Join Date
    Sep 2010
    Location
    Atlanta, GA
    Posts
    19
    Post Likes
    Quote Originally Posted by Keith73 View Post
    I'll keep it brief.

    My Situation: offer support and guidance to other techs.

    My Question: Your oppinion on the actuall use of nitrogen and micron gauges in the field. What percentage of techs actually do as they are instructed.

    It can be obvious at times during follow-ups what was not done or done wrong.
    I am the technical training manager in a large atlanta based company. We regularly inspect our 30 plus techs tools and practices. we use micron guages on every system we open and purge with nitrogen. Some may try to cut corners but we pay them well enough and we check up on them and the customers fill out our survey cards.

  3. #3
    Join Date
    Apr 2006
    Location
    mechanical room
    Posts
    1,790
    Post Likes
    opinion no, it is second nature

  4. #4
    Join Date
    Oct 2001
    Location
    Stoney Creek, Ontario
    Posts
    885
    Post Likes
    been doing markets for 20+ years, have never seen a N2 purge on any install

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by shaun66 View Post
    been doing markets for 20+ years, have never seen a N2 purge on any install
    I haven't been doing it that long, but I've not seen n2 on an install, either.

    Micron gauges, yes, but nitrogen no.

    Not dismissing the importance of it, its use would make life a lot easier for the start-up guy, just stating facts.
    Last edited by jpsmith1cm; 10-03-2010 at 05:23 PM. Reason: typo



  6. #6
    Join Date
    Oct 2001
    Location
    Stoney Creek, Ontario
    Posts
    885
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    I haven't been doing it that long, but I've not seen n2 on an install, either.

    Micron gauges, yes, but nitrogen no.

    Not dismissing the importance of it, its use would make life a lot easier for the start-up guy, just stating facts.
    I am the startup guy, rarely get a tx screen plugged, maybe 1 screen in every 10 rack startups.

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by shaun66 View Post
    I am the startup guy, rarely get a tx screen plugged, maybe 1 screen in every 10 rack startups.
    WOW!

    Your fitters must be good.


    Start 'em, let 'em run a day, come back and clean screens and set TXVs.

    That's how we do it.

    Well, that or throw the valves and cross our fingers that everything works which is how some others prefer to operate.



  8. #8
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    (This thread should be moved to Refrigeration & Icemaking...or at least Commercial.)

    It rather surprises me that you two very experienced market techs have never seen nitrogen purge on installations.

    Way back in the mid 1980s, when I was in charge of installations for a chain in New England, we had as part of our written installation specifications that a nitrogen purge shall be used at all times during brazing.

    Further, the specs stated that we had the right to cut out, at random, any fitting in the system to inspect it for oxidation and scaling. If the inspection failed, we could call for the entire system to be redone.

    A full repipe never happened to my knowledge, but there were cutouts done.

    I'll have to dig out a copy of those old specs and post them.

    As a matter of fact, I had a new contractor on a job who when I showed up unannounced for a site check, they reviewed their N2 setup and policy with me. I couldn't help but noticed the 10-12 large nitro cylinders stocked in the back room.

    They actually had two test fittings ready for me, showing the difference between brazing with nitrogen and without.

    I never bothered them after that about purging...and the startup socks in the suction filters were as clean as I've ever seen.

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by icemeister View Post
    (This thread should be moved to Refrigeration & Icemaking...or at least Commercial.)

    It rather surprises me that you two very experienced market techs have never seen nitrogen purge on installations.

    Way back in the mid 1980s, when I was in charge of installations for a chain in New England, we had as part of our written installation specifications that a nitrogen purge shall be used at all times during brazing.

    Further, the specs stated that we had the right to cut out, at random, any fitting in the system to inspect it for oxidation and scaling. If the inspection failed, we could call for the entire system to be redone.

    A full repipe never happened to my knowledge, but there were cutouts done.

    I'll have to dig out a copy of those old specs and post them.

    As a matter of fact, I had a new contractor on a job who when I showed up unannounced for a site check, they reviewed their N2 setup and policy with me. I couldn't help but noticed the 10-12 large nitro cylinders stocked in the back room.

    They actually had two test fittings ready for me, showing the difference between brazing with nitrogen and without.

    I never bothered them after that about purging...and the startup socks in the suction filters were as clean as I've ever seen.

    Ice,

    It's STILL in the job specifications that I've read, exactly as you describe it. Nitrogen purge MUST be used and the customer has the rights as you described.

    I just think that some customers are much more lax about enforcement than others.

    I can remember hearing some of the fitters b***h about jobs where the HAD to do the purge in cases where the customer was not lax about enforcement.

    About all that is done is to verify the presence of nitrogen on the jobsite. Doesn't matter if it's used or not, just has to be there.



    Part of the problem may have something to do with the evolution of the rack system as I'm seeing it.

    We aren't seeing the 'standard' system anymore. By 'standard' I mean one liquid line and one suction line from the rack to the case. In this case, particularly during a remodel, it is easy to set up a purge and to do it.

    Newer systems are 'looped' systems with a large liquid line or two or three running through the store with similarly large suction lines paralleling them and EEPR valves controlling the individual circuits.

    Much harder to use a nitrogen purge in this type of arrangement as there are fewer access points and those that exist are harder to access to use as a point for introducing nitrogen to the system.


    Then again, maybe contractors have gotten cheaper and fitters have gotten lazier.


    I'm not sure which is the case.



  10. #10
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    543
    Post Likes
    Thread Starter
    I apreciate everyone's feedback! I hope to get more.

  11. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,743
    Post Likes
    The old refrigerants and oils were very forgiving. As JP said run the systems for a day and pull and clean the screens was SOP.

    POE oil changed all that. POE is a solvent as it circulates through the system. Scale that would probably stay put before is now flushed down stream.

    JP I would suggest changing suction filters and cleaning the strainers on the pumps as well. You’ll be surprised at the amount of crap in them.

  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by pecmsg View Post
    The old refrigerants and oils were very forgiving. As JP said run the systems for a day and pull and clean the screens was SOP.

    POE oil changed all that. POE is a solvent as it circulates through the system. Scale that would probably stay put before is now flushed down stream.

    JP I would suggest changing suction filters and cleaning the strainers on the pumps as well. You’ll be surprised at the amount of crap in them.
    Yep.

    Big pressure drops across driers and filters.

    The refrigerant and oil technology has moved on and, sadly, some have chosen to not keep up with the technology.

    What I described is still being practiced on R-404a rack systems.



  13. #13
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,486
    Post Likes
    have never purged with N2 during install or service repairs.

    always use micron gauge to ensure a proper vacuum is pulled. If your techs are cutting this corner, it may be in part to lack of training to proper procedures and methods to pull a fast good vacuum. Utilizing 3/8's hoses, removing schrader cores, and a vacuum "tree" versus a manifold will cut vacuum times in half!
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

  14. #14
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    543
    Post Likes
    Thread Starter
    I agree with the vacuum of course but without using N2, it is still cutting corners.

    Nitrogen keeps the system clean and also purges contaminates.

    Did I mention it prevents carbon deposits from brazzing?

  15. #15
    Join Date
    Oct 2010
    Location
    Austin, TX
    Posts
    1,381
    Post Likes
    I haven't found a company yet that would except the expense of using N2 while brazing.

    I agree whole heartedly with N2 while you braze, before you vacuum, and requiring techs to use a micron gauge. I am so fanatic about my own micron gauge I used a cigar box and foam to make it a protective case.

    Last edited by XcelTech; 10-05-2010 at 09:58 PM. Reason: Added pictures

  16. #16
    Join Date
    Apr 2010
    Location
    NYC
    Posts
    505
    Post Likes
    It's Terrible for me to say but most companies would pay for the nitrogen, instead of leaving the pump over night. And following up next day losing hours.

    Unfortunatly the customers up here just think its normal to change a compressor every five years.
    Spend spend especially now,, right before xmas
    I don't even think the customers ask y did my compressor go.??

    I don't agree with this Practice


    Maybe ill start a kickback thread

  17. #17
    Join Date
    Oct 2001
    Location
    Stoney Creek, Ontario
    Posts
    885
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Yep.

    Big pressure drops across driers and filters.

    The refrigerant and oil technology has moved on and, sadly, some have chosen to not keep up with the technology.

    What I described is still being practiced on R-404a rack systems.
    driers and filters are always changed after couple days run time, covered in black. they did their job

  18. #18
    Join Date
    Sep 2007
    Posts
    31
    Post Likes
    If the line set is less than 100 ft we will not use N2 to purge. However, in supermarkets we always use N2 regardless of the length of pipe. Afterwords we always throw a pump with a micron gauge on it.

  19. #19
    Join Date
    Jul 2009
    Location
    new york
    Posts
    928
    Post Likes
    Quote Originally Posted by XcelTech View Post
    I haven't found a company yet that would except the expense of using N2 while brazing.

    I agree whole heartedly with N2 while you braze, before you vacuum, and requiring techs to use a micron gauge. I am so fanatic about my own micron gauge I used a cigar box and foam to make it a protective case.

    Might as welll put that in a pelican case and lock box Ive seen it all--olololololololololololololololololol

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •