    habco esm12 keeps going off on overload

    working on neighbours cooler he uses for beer

    first showed up and compressor not starting and tripping overload
    remove start cap , current relay and overload
    install supco 3 in 1

    unit short cycled with thermostat
    temporary bypass thermostat and test
    unit runs for 1 minute then trips on overload

    remove condensing unit and test on bench next day, unit ran for 15 minutes contious
    re-installed unit and installed electronic refrigeration thermostat

    unit still tripping on overload after 1 minute roughly

    R 134a unit running pressures 25 psi suction, 110 psi discharge

    ohmed out compressor windings and turned out good

    im out of ideas anyone else have anything i have missed ???

    ps i suck at posting please be nice

  2. #2
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,156
    Post Likes
    Pressures look fine for a warm box

    Have you performed Amp draw test ?

    Sounds like the compresors been thru hell and probly hurting on the electric part of it

  3. Likes icemeister liked this post
  4. #3
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,318
    Post Likes
    Common issue is guys use the RCO410 start 3n1 which is for a 1/4hp and has a max amp draw of 7amps. They put it on 1/3hp compressors that draw 7 or 8 amps. After about a minute it trips overload. Look up the max amp draw on the 3n1 you installed and compare. May just have the wrong 3n1 on it. The RCO210 handles up to 1/2hp and will run a higher continuous amp draw.

    Sent from my SAMSUNG-SM-G890A using Tapatalk

  5. #4
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,156
    Post Likes
    Those 1/3 ... 1/4 are only good for residential fridges, and barely do those

  6. #5
    Join Date
    Jan 2010
    Posts
    12,415
    Post Likes
    Quote Originally Posted by trippintl0 View Post
    The RCO210 handles up to 1/2hp and will run a higher continuous amp draw.
    Maximum RLA 13.3 amps.

  7. #6
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    12,486
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    Pressures look fine for a warm box

    Have you performed Amp draw test ?

    Sounds like the compresors been thru hell and probly hurting on the electric part of it
    Agreed. I'd suspect a bad overload...especially on these little compressors with low starting torque that many OEMs use these days (ie, no start cap). They don't qualify for commercial duty in my book.

  8. #7
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    7,708
    Post Likes
    Just sort of wondering what the head pressure goes up to just before it kicks out.

  9. #8
    Join Date
    Apr 2011
    Location
    stratford ontario
    Posts
    30
    Post Likes
    Running Amps measured 4.5,
    110 psi discharge pressure when it runs and kicks out

  10. #9
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    7,708
    Post Likes
    bigger 3 and 1

  11. #10
    Join Date
    Apr 2011
    Location
    stratford ontario
    Posts
    30
    Post Likes
    Compressor is a techumseh
    Ae 540 ar 277b6

  12. #11
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,318
    Post Likes
    Head pressure is low for a normal ambient. Is this in a cold garage? (Edit) ok well maybe not that low. Usually I see 150# head. But that's in a commercial kitchen. (/edit)

    Have you figured out which 3n1 you installed and what it's max amp draw is? 4.5 isn't very much amps, unless you have like the 3n1 for an 1/8hp. The rco810 has max amp draw of 4.05a.

    Sent from my SAMSUNG-SM-G890A using Tapatalk

  13. #12
    Join Date
    Apr 2011
    Location
    stratford ontario
    Posts
    30
    Post Likes
    R c o 410 is what I used , and wasn't really cold in the garage has electric heater running

  14. #13
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    11,871
    Post Likes
    6.8 rating on that model but wouldn't be the first bad out of the box. What was the pump drawing?