    Solenoid valve ?

    Why would you install a solenoid on a equalizer line for a hgbp valve ?

  2. #2
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,596
    Post Likes
    On the actual hot gas line itself??

  3. #3
    Join Date
    Jun 2010
    Posts
    133
    Post Likes
    No , I know you need one there for isolation when you have a LLSV this is on the pilot tube -equalizer line

  4. #4
    Join Date
    May 2003
    Location
    Utah
    Posts
    758
    Post Likes
    Theres no reason to put a SV in the equalizer line.

    What controls the SV?

  5. #5
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,747
    Post Likes
    Quote Originally Posted by newbe0507 View Post
    Why would you install a solenoid on a equalizer line for a hgbp valve ?
    To turn the HGBP off would be my guess.

  6. #6
    Join Date
    Jan 2010
    Posts
    8,176
    Post Likes
    Quote Originally Posted by Dallas Duster View Post
    To turn the HGBP off would be my guess.
    That's done on the hot gas bypass line itself.

  7. #7
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,596
    Post Likes
    A picture sure would help, cause it isn't making much sense to me why you would do that.

  8. #8
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,747
    Post Likes
    Quote Originally Posted by VTP99 View Post
    That's done on the hot gas bypass line itself.
    Would you give me the same answer for a TXV? For capacity control in multiple TXV applications coil?

  9. #9
    Join Date
    Jan 2010
    Posts
    8,176
    Post Likes
    Quote Originally Posted by Dallas Duster View Post
    Would you give me the same answer for a TXV? For capacity control in multiple TXV applications coil?
    Are you asking about a EPR ?

  10. #10
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,747
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Are you asking about a EPR ?

    Nope a plane ole TXV . What's going to happen to the TXV if we turn the equalizer off to it?

  11. #11
    Join Date
    Jan 2010
    Posts
    8,176
    Post Likes
    Quote Originally Posted by Dallas Duster View Post
    Nope a plane ole TXV . What's going to happen to the TXV if we turn the equalizer off to it?
    Your going to lose one of the three forces operating the TXV. Has nothing to do with hot gas bypass. Show me one piping diagram for hot gas bypass using a solenoid on the TXV equalizer line.

  12. #12
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,747
    Post Likes
    Is that even possible what if you don't have a MLV on the circuit?


    Quote Originally Posted by VTP99 View Post
    Your going to lose one of the three forces operating the TXV. Has nothing to do with hot gas bypass. Show me one piping diagram for hot gas bypass using a solenoid on the TXV equalizer line.

  13. #13
    Join Date
    Jan 2010
    Posts
    8,176
    Post Likes
    Quote Originally Posted by Dallas Duster View Post
    Is that even possible what if you don't have a MLV on the circuit?
    Well now the OP never did say what application he was looking at. My guess is a freezer which should have a CPR. As far as a MLV (minimum load valve ) I would expect to see one of those on a chiller application. There the MLV equalizer line would be teed into the TXV equalizer line. With a solenoid on the discharge side of that valve.