Duct Board Question
I am doing a microwave install for a buddy. I pulled out the old range vent to put in a new microwave. The vent pipe is just a few inches above the cabinet bottom. The microwave vent is triangle. There is nothing that will convert and bend that short. Will duct board be ok to use for this. It is above the oven.
-
09-24-2010, 11:01 AM #2
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,316
The major issue here would be cooking grease collecting on the ductboard... which would be a fire hazard if it ignited... or if there was a fire on the range below and the vent caught. Vents for cooking hoods and appliances should ALWAYS be metal.
You may have to 'custom fabricate' a fitting, or cut some of the existing pipe and install a pre-made fitting.
I would NOT use anything other than metal, and I would be careful the joints between fittings do not have any gaps.GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
09-24-2010, 11:05 AM #3
Thats what I was guessing here. The opening from the microwave to the vent is so close. Ill have a buddy fabricate a metal box that I can just slip in. Safest way. Thanks
-
09-25-2010, 03:03 AM #4
Banned
- Join Date
- Aug 2010
- Location
- Seattle Wa.
- Posts
- 168
never use duct board for anything
-
09-25-2010, 09:45 AM #5
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,316
For me, ductboard makes good return plenums in non-humid locations (never in a crawl). Easy for an attic when replacing a dedicated horizontal and adding a media filter to the new furnace.
Personally, I never use ductboard after the air filter... just a matter of principle.GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
09-25-2010, 01:06 PM #6
Professional Member*
- Join Date
- Sep 2010
- Location
- LA
- Posts
- 99


Reply With Quote
. There is nothing that will convert and bend that short. Will duct board be ok to use for this. It is above the oven.