    Need help on an old R-22 Lennox unit (my house)

    Hello, new to the forum, and thanks in advance for your help.
    Just bought a house:

    I have a REALLY old Lennox 4 ton R-22 outdoor unit (prob about 15+ years old) with a newer 4 ton indoor air handler unit (about 6 years old) AC ONLY, Not a Heat Pump...

    The Lennox outdoor unit has failed (given up) I have a brand new 3 ton 12 seer R-22 Goodman outdoor unit Would this work on a 4 ton air handler? The house is only 1300 sq ft.

    This would be a temp fix, untill I raise enough money to install a R410A System.

    Please give me your input on if this would work as a temp cooling fix?

    Again, Thanks for all of your help
    Mike

  2. #2
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    Nope, the evap. coil will need to be changed as well as blower speed.

  3. #3
    Join Date
    Sep 2009
    Location
    S.C.
    Posts
    1,441
    Post Likes
    Mikey, Your post Lennox with the Dead 4 ton unit is exactly what I quoted on about 2 weeks ago.

    It "sounds" like your system was Over-sized... for a 1,300 sf home, unless you don't have any insulation or doors? The good thing is, if you are going for a Temporary Fix (which tends to be permanent) and we just entered into Fall. Before you spend any money you need to have a Manual J calculation done. Call a Contractor and get them to look at your house/system and see what's the best direction to go. A "good" Tech can make a 3 ton condenser work with your 4 ton air handler (but there's things that have to be changed).

    Also, Mike
    Yes, I know I Shouldn't But I Just Can't Help Myself...

  4. #4
    Join Date
    Sep 2010
    Location
    Virginia
    Posts
    3
    Post Likes
    Thread Starter
    I am an HVAC tech (been out of the field for awhile (3 years) since I am an office engineer But I am very knowledgeable in HVAC (5 years in the field///ex military)I have all the equipment (vacc pumps, recov machines, guages, torches, etc.etc. in my shed) I think I am knowledgeable in the field done over 50 comp change outs (1 phase/ 3 phase R-22 and limited on the R-410A) Back in the day But I am obviously Universal certed, and have my old cert card.

    So I know enough to get into trouble

    short story, I am broke (3 kids in college) and my wife has been sick for over a year, so she is not working. So, Yes this will have to hold me over for about 2 years, until I can at least get 2 of the 3 out of school to free up some income..

    any advise to make this work would be a huge help (knowing the right way would be to swap the inner coil to match the 3 ton) But what would be the key to make this work.

    AGAIN<<< THANKS SOOOOO MUCH FOR YOUR TAKING THE TIME TO HELP ME OUT

    Regards,

    "Mikey"

  5. #5
    Join Date
    Sep 2005
    Posts
    58,704
    Post Likes
    OK, here is what will happen if you do what you plan to do...

    You will have a mis-match that will not cool well, will be humid, and will use WAAY too much elec. There are other issues also... call a Pro out and they will explain them.

    It will be a temp repair... It may (and may not) last long enough to get the $$$ together for a new system.

    My advise is to not try to go the 'thrifty' route here... rather just take the plunge and get a new system. What usually happens with these 'mis-match repairs' is too much $$$ is spent on the mindset of 'saving a buck by doing _____'. This same $$$ could be applied to a new unit, which would perform a lot nicer.

    Oh, and if you are married, will your wife see the 'thriftyness' of this... or will she fuss about the thing not working properly... Might want to think about this also...
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  6. #6
    Join Date
    Oct 2004
    Location
    Yakima, WA
    Posts
    1,847
    Post Likes
    Will it work, will it cool? Maybe, even probably. Will it work properly and be any kind of efficient? You know the answer to that already. This is an open forum and DIY advice can't be given here. I understand you are experienced in the field, but it is what it is.

    I will tell you this, several things need to be addressed and may have to be changed: metering, lineset size, airflow, charge... it will need to be dialed in to as good as it will get but know that it will probably never look perfect.

    If it doesn't work at all and you are out $100 in parts, I say it was a worthwile experiment. If its going to be hundreds I would probably step back and craigs list that unit you have. You wouldn't ever do this for a customer, but you don't have the $ to "take the plunge" now or in the next couple of summers - reality is what it is. If it were me I would give it a try.

    Just remember temporary is temporary and start filling that coffee can with dollars as soon as you can!

  7. #7
    Join Date
    Sep 2010
    Location
    Virginia
    Posts
    3
    Post Likes
    Thread Starter
    Well, I appreciate all the help. And thanks for the honest opinions. Yes. It is what it is. Fortunatally the new Goodman unit was a left over that was sitting in the warehouse, and was basically given to me. So other than about $100.00 in parts (you are correct) It is worth a try. knowing that in teh next 1.5 years my 12k a month in tuition fees (for my kids) will go down to about4K a month when the 2 oldest graduate:P

    Yes, I will dial it in (as best as poss) for the tonnage difference and in the mean time, put money in the coffers for a new system. I just need to suffer for another 1.5 years until the little ones get through school.

    Thanks again for the $.02

    If you all would like, I can post and let you know how it works out..

    My best regards

    Mike

  8. #8
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,527
    Post Likes
    FRANKENUNIT!

    There are ways to make it work fairly well. A good tech will know what to do to get the superheat in the proper range so the compressor won't be damaged.

    The unit may not dehumidify well, but if had a 4-ton unit in a 1300 sq. foot house you're probably used to feeling muggy.

  9. #9
    Join Date
    Jun 2010
    Location
    Danbury Ct 1/2 hour from NYC
    Posts
    204
    Post Likes
    couldn't have said it any better!! 1300 sq with 4 tons is some clammy cooling, he should lower the fan speed on the AH

  10. #10
    Join Date
    Sep 2009
    Location
    S.C.
    Posts
    1,441
    Post Likes
    Sure Mike, tell us how it works out. From what you've said experience wise, you know what to try. I'm still puzzled by the 1300 sf and 4 tons.

    12k tuition monthly... Geeeee whiz, that hurts.
    Yes, I know I Shouldn't But I Just Can't Help Myself...

  11. #11
    Join Date
    Jun 2009
    Location
    Bakersfield, Ca
    Posts
    1,716
    Post Likes
    Quote Originally Posted by Pilot1 View Post
    Well, I appreciate all the help. And thanks for the honest opinions. Yes. It is what it is. Fortunatally the new Goodman unit was a left over that was sitting in the warehouse, and was basically given to me. So other than about $100.00 in parts (you are correct) It is worth a try. knowing that in teh next 1.5 years my 12k a month in tuition fees (for my kids) will go down to about4K a month when the 2 oldest graduate:P

    Yes, I will dial it in (as best as poss) for the tonnage difference and in the mean time, put money in the coffers for a new system. I just need to suffer for another 1.5 years until the little ones get through school.

    Thanks again for the $.02

    If you all would like, I can post and let you know how it works out..

    My best regards

    Mike
    Sweat it out for another year and when your kids are astronauts and city planners, they can pay you back and you will be able to afford a good quality 3 ton Tempstar!

  12. #12
    Join Date
    Nov 2009
    Location
    Saskatchewan
    Posts
    494
    Post Likes
    Believe it or not, yes. I do not sell stuff like this, but have butched a couple for property management guys with a collection of odds and ends. On a temp fix until a new system can be ready. IE ( keep the old split going until we can upgrade to a new RTU and duct in the fall )

    You would be amazed what works. It is doable with the right McGiaver.

  13. #13
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    12k a month???????????????????????


    you must have a great job!!!!!!!!!!!!!!!

    tell one of the kids to miss a semester and buy a complete new system!!!!!!!!!!!
    true knowledge exists in knowing that you know nothing.

  14. #14
    Join Date
    Jun 2003
    Location
    Hell Hole Swamp
    Posts
    4,255
    Post Likes
    Temporary fix, sure, be best to set the fan to a lower speed and change the orifice to the proper size for the outdoor unit, or install a TXV

    lol at those that say it wont work

  15. #15
    Join Date
    Mar 2007
    Location
    Madison, Wisconsin
    Posts
    2,749
    Post Likes
    If the AH has a multi speed motor, change cooling to low speed, and add a TXV, should work if you can dial in that charge.
    I r the king of the world!...or at least I get to stand on the roof and look down on the rest of yall

  16. #16
    Join Date
    Sep 2010
    Location
    LA
    Posts
    202
    Post Likes
    I agree with WB and others; it will work for the temporary with the proper adjustments and might even find better RH in house with more runtime...to bad about the cash outlay. If you could swing finances you could get a new system that would save you $$ and get the $1500.00 tax cedit to boot! Its like getting $1500 off your purchase price. Alas, it goes Bye-bye 12/31/10...

  17. #17
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    it may already have a txv?
    it may also be the correct one?
    true knowledge exists in knowing that you know nothing.

  18. #18
    Join Date
    Sep 2008
    Location
    VA
    Posts
    6,217
    Post Likes
    Oversized airhandlers are common practice usually gaining SEER points in some cases. The mismatching is a little concern, but more so with a heat pump, in which you've stated you do not have. Most all recent residential Lennox airhandlers come equipped with TXVs. The only issue is that 3 tons of cooling in a 1300 sq home??? I guess we can't presume anything without seeing the actual load though. It's certainly better than the 4 tons that you're removing though. Good luck, just make sure you practice proper cleanup if the old unit was a "burnout" compressor.

  19. #19
    Join Date
    Feb 2001
    Posts
    35,834
    Post Likes
    If the indoor coil has an expansion valve it will work ok.

    Hook it up, whadda ya got to lose?
    Hey cockroach, don't bug me! ©

  20. #20
    Join Date
    Oct 2009
    Location
    new jersey
    Posts
    621
    Post Likes
    Goodman uses a bigger coil than the condenser. Try an expansion valve. I bet it will work long enough to get by.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •