    Trane XL 16i - Problem with Heating

    I have a Trane heat pump system XL 16i, outdoor model# 4TWZX6036B1000AA indoor model# 4TEE3F37B1000AA controlled with Honeywell VisionPro IAQ (YTH94Z1C1002) thermostat. The backup is electric strips.

    I've had the system since 2007 and it's worked pretty well so far. However, today, I noticed a strange thing: the heat pump has been running all morning (from about 6:00am and it's about noon now), yet the temperature dropped from 69 to 66F. The thermostat is set to 70F and outside temperature currently is fairly mild 53F.
    In the past, I experienced the situation where the heat pump couldn't keep the set temperature by itself but never when it was in the 50's outside. (the last time it happened the outside temps. was definitely below 30F).

    I figured that maybe the filters were too dirty (although I clean them regularly and they didn't need to be cleaned yet per the indicator) so I cleaned them about 2 hours ago. That didn't make any difference - the heat pump keeps on running and the temp. sits at 66F.

    Does anyone have an idea about what the problem may be?

    Thanks.

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Not much we can suggest without seeing it. SHUT IT OFF to avoid damage to it and call a tech.

  3. #3
    Join Date
    Jul 2010
    Location
    DFW -> Texas
    Posts
    446
    Post Likes
    Whens the last time you had the unit serviced? It may just need to be serviced.

  4. #4
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    that stat will overcool to dehumidify by 3 degrees

    what is your humidity setpoint at



    .

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Airmechanical View Post
    that stat will overcool to dehumidify by 3 degrees

    what is your humidity setpoint at



    .

    With it set to heat mode, or even in auto mode. It won't over cool to dehumidify. In auto, the last call has to have been for cooling for it to do a dehumidify call.

  6. #6
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    Quote Originally Posted by beenthere View Post
    With it set to heat mode, or even in auto mode. It won't over cool to dehumidify. In auto, the last call has to have been for cooling for it to do a dehumidify call.
    thought he was in cooling mode, my bad, i did not pay atention

    yes, he needs to tech



    .

  7. #7
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    543
    Post Likes

    Professional Service

    I agree, call a technician. The system may not be activating the second stage for a number of reasons.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •