    rthc oil sump level check

    i am reading an iom manual and it says the following.,

    1 Attach the 3/8” or 1/2” hose with a sightglass in
    the middle to the oil sump drain valve and the
    condenser service valve at the top of the
    condenser.

    2 After the unit is off line for 10 minutes move the
    sightglass along the edge of the condenser tubesheet at the same height of the oil sump
    .

    why would one move across condenser tube sheet anyways?,
    my question is that if one moves the sight glass along the cond tube sheet,,
    at the same height of the oil sump??

    trane .com
    rthc-iom-1c
    page 129 or 9-1

    thanks

  2. #2
    Join Date
    May 2008
    Location
    Central Pennsylvania
    Posts
    443
    I didn't look at the IOM to see how it was worded, but I think it just tells you that because you can't really get to the oil sump since it's behind the condenser. Do youself a favor and do as some of the other guys on this site have. Go to a hose shop and have a piece of clear high pressure hose made up to use as you siteglass. I had two made up, one for poe and on for mineral oil. 12" long with 1/4" male flare fittings on each end so you can hook them to standard refer hoses, works great!

  3. #3
    Join Date
    Mar 2007
    Posts
    3,134
    Is it just me, or is that the worst possible location for the oil sump on that machine. I am very glad there aren't many RTHC units in my area, because they can be a real pain in the @$$. The RTHD is a vast improvement, IMO
    The key to happiness is lower expectations.

  4. #4
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,111
    Quote Originally Posted by chillerguy81 View Post
    I didn't look at the IOM to see how it was worded, but I think it just tells you that because you can't really get to the oil sump since it's behind the condenser. Do youself a favor and do as some of the other guys on this site have. Go to a hose shop and have a piece of clear high pressure hose made up to use as you siteglass. I had two made up, one for poe and on for mineral oil. 12" long with 1/4" male flare fittings on each end so you can hook them to standard refer hoses, works great!
    well that explains it ., lol thanks.,
    as far as a hose shop, im tring to find one., should i go online.,

  5. #5
    Join Date
    May 2008
    Location
    Central Pennsylvania
    Posts
    443
    Quote Originally Posted by mlkwal1 View Post
    well that explains it ., lol thanks.,
    as far as a hose shop, im tring to find one., should i go online.,
    I would think you could find something local, try a shop that sells hydraulic hoses, fittings, and such.