11-28-2012, 01:50 PM #27
subcooling??
B[COLOR=a friend is one who knows us , but loves us anyway
-
11-28-2012, 09:44 PM #28
You guys must really exel at making things way more difficult than they need to be. If you are using condensate from the evap coil, there are no minerals to contend with and it's the same as if it started to rain on the unit.
Government is a disease......masquerading as its own cure…Ecclesiastes 10:2 NIV
-
11-29-2012, 12:20 AM #29
Last edited by zartangreen; 11-29-2012 at 12:41 AM.
-
04-07-2013, 01:26 PM #30
New Guest
- Join Date
- Apr 2013
- Posts
- 2
I just love some of the unproductive responses some give...
It amazes me how many sites like this get individuals with such unproductive answers that help no one. To those that seem to think they know what the outcome will be why dont you actually try it before talking? The only thing I agree with is you will get deposits on your cond coil but it takes some time before the deposits are substantial and there is this miraculous new invention called DESCALER or LIME AWAY. Works wonders on lime deposits very quickly. Needless to say I have tried the mist technique. First on a friends P.O.S AC unit which was way too underpowered for his Apt. It couldn't bring down the temp inside if the doors were opened too often. For the hell of it I put a mister with an in line filter on it and there was an immediate and drastic difference on its cooling capability. After seeing this I did it to my house. It does have an older 3.5 ton on it but with a new compressor. I didnt feel like having flood waters around the house so it was connected to a water valve so it only turned on with the AC and not set up to hose the unit, just mist the coils only. Worked well there too. Ever see the cooling towers at hotels? Whats the purpose of them if water cooling is such a bad idea? Maybe you just need some creativity. Also, Obviously Electricity and water are bad to mix, so dont.. its not that hard and what happens when it rains? People dont get electrocuted then..... Put a little thought in your responses people.
-
04-07-2013, 02:13 PM #31
Spraying or misting mineral latent water on to an air cooled cond coil is like giving it a crack pipe. It wil be very happy and feel real good. It will however develop an addiction. It will eventually refuse to operate without it as well as demand more and more. The minerals will plate out on the coil insulating it requiring more water and so on. The cooling tower comparison is invalid due to application. A cooling tower flows warm water over the fill, same temp as the water, and air is drawn through to absorb the heat from the water. Cool water sprayed onto a hot coil will cause the minerals to plate out much much faster and directly onto the coil.
-
04-07-2013, 02:32 PM #32
-
04-07-2013, 03:11 PM #33
Misting with other than water from condensate or demineralized water is just not a prudent thing to do. I can understand the mind set that without misting, the system just doesn't keep up with the heat load, but one must understand that by doing so there will be consequences.
Government is a disease......masquerading as its own cure…Ecclesiastes 10:2 NIV
-
04-07-2013, 03:25 PM #34
Professional Member
- Join Date
- Jul 2000
- Location
- Dallas,Texas
- Posts
- 4,806
-
04-07-2013, 04:53 PM #35
Misters do work, but they should NOT be sprayed onto the coil, they should spray mist away from the coil "Opposite to the air flow". The object is to bring down the dry bulb temperature, not to wet the coil. The spray is vapourised, the TDS (total dissolved solids) becomes effectively dry dirt that passes through he coil block.
-
04-07-2013, 05:14 PM #36
Professional Member
- Join Date
- Dec 2011
- Location
- bedford ind
- Posts
- 1,080
last time i checked, de-scaler and lime away, were not to be used on aluminum.
-
04-07-2013, 05:20 PM #37
Professional Member
- Join Date
- Dec 2011
- Location
- bedford ind
- Posts
- 1,080
wouldn't all the stuff that is causing such corrosion on the indoor coils be present in the condensate, thereby causing corrosion on the o.s. coils ?
Last edited by ironpit; 04-07-2013 at 05:22 PM. Reason: for robo
-