    Sandwich bar sweating badly.

    Have an r-22 sandwich bar sweating profusly. What kind of evap temp should I be running and what about sh? It has a single evap w/dual fans that blow the air up from the refrig compartment to the sandwich bar.
    Thanks

  2. #2
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301
    Lowest coil temp should be around 20F with evap cycling above freezing during temp satisfaction phase or during defrost long enough to melt any ice accumulation on evap fins. Are the gaskets ok? Is room temp under 86F(?), and they must keep the lid down for proper temp and moisture control between uses. It's built for the lid to stay closed whether it's a pain fopr them or not. you can only control the machine not the customer!

  3. #3
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    5,316
    Also consider that the dew point in space is excessively high. 75^F, 50%RH, 55^F dew point space conditions means that if the surface temperture of the sandwich bar is below 55^F, the surface will be wet. Lowering the dew point of the air around the bar or raise the temperature of the bar a couple degrees are solutions. Increasing dehumidification by the a/c requires lower air flow and a colder a/c coil is a possible solution. Adding a good dehumidifier like the Ultra-Aire is solution if your a/c is not operating enough to lower the dew point.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  4. #4
    Join Date
    Apr 2002
    Location
    Western piedmont of Carolinas
    Posts
    1,214
    Thanks you. I think it's more of a drain issue, just wanted to rule out anything in the refrig cycle. Replaced the pan a couple yrs ago, but new one wasn't 100% o.e.m. so had to use duct tape to rig it. Thanks again.

  5. #5
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301

    Hmm

    Quote Originally Posted by mlock View Post
    Thanks you. I think it's more of a drain issue, just wanted to rule out anything in the refrig cycle. Replaced the pan a couple yrs ago, but new one wasn't 100% o.e.m. so had to use duct tape to rig it. Thanks again.
    DUCT TAPE! tHE BANE OF ANY GOOD TECH. Anything worthy doing is worth doing right.