Mitsubishi 12,000 btu with hyper heat (mszfe12na)
First post here it goes!
Finishing a Bonus room for a customer. 16X24 room dims with a 4 ft knee wall 30 degree angle ceiling with a max height of 8 ft. The room is spray foam insulated. i advised customer Mitsubishi 12,000 btu with hyper heat (mszfe12na) should be sufficient for this room size and how well it is insulated. However they had H-vac guy out to quote and he says it needs a Mitsubishi 22,000 btu mini split!!! i thinks it a little over kill... any advise??
climate is Northern Ohio...
give me some advise experts.
-
08-23-2010, 11:37 AM #2
Professional Member
- Join Date
- Sep 2007
- Location
- Tucson AZ
- Posts
- 19
That's easy, run a heat load calculation and you'll know who is correct!
-
08-23-2010, 12:54 PM #3
Regular Guest
- Join Date
- Aug 2010
- Posts
- 6
Heat load
i did and came up with right around 11,000 btu's. Just wanted to make sure someone else could confirm this since i am no HVAC Professional.
-
08-23-2010, 01:18 PM #4
I would listen to the hvac professional. How cold does it get in O-Hi-O?
My doctor gave me six months to live, but when I couldn't pay the bill he gave me six months more.
Walter Matthau
-
08-23-2010, 02:14 PM #5
Professional Member
- Join Date
- May 2008
- Location
- Portland, OR
- Posts
- 236
Was your heat load 11k cooling or 11k heating?
The contractor may have recommended a larger unit for the purposes of heating the room instead of cooling.
Great system by the way!
-
08-23-2010, 02:34 PM #6
Regular Guest
- Join Date
- Aug 2010
- Posts
- 6
yeah I'm sorry.... that was for cooling (with fiberglass insulation) .... i can i get some help for heating?
-
08-23-2010, 02:37 PM #7
Professional Member
- Join Date
- May 2008
- Location
- Portland, OR
- Posts
- 236
16x24, 8ft ceiling
How many, what size and what type of windows?
What's the R-value of the insulation in the ceiling and walls?
What kind of floor is it (crawl-space, cement, basement)?
What kind of flooring (wood, carpet)?
What's the zip code?
With this information I can run a heat load for you. =)
-
08-23-2010, 02:58 PM #8
Fujitsu I might do A 22,000 as well. With the inverter varaible capacity 9900-27300 I wouldnt worry about being over sized in cooling.
i belong to peta ... people eating tasty animals. all my opinions are just mine.
-
08-23-2010, 04:13 PM #9
Regular Guest
- Join Date
- Aug 2010
- Posts
- 6
24x16
No windows
walls r-15
ceiling r-50
insulated garage below
carpet on the floor
zip 44883
-
08-23-2010, 04:43 PM #10
Professional Member
- Join Date
- May 2008
- Location
- Portland, OR
- Posts
- 236
I'm getting 11k heating, 6.6k cooling.
The colder it gets outside, the less efficiently the mini-split will work. Oversizing the system will compensate for the up to 30% loss in capacity when it gets cold.
I agree with the contractor. A 22k system would be the best option. A 12k would work most of the time, but may not produce enough warm air on the coldest days.
-
08-23-2010, 04:53 PM #11
Regular Guest
- Join Date
- Aug 2010
- Posts
- 6
That's why i was thinking the mszfe12na with muzfe12na with the hyper heat holding efficiency down to the single digits.....
Maybe just go with the bigger size then not disappointed!
-
08-24-2010, 12:31 PM #12
Regular Guest
- Join Date
- Aug 2010
- Posts
- 6