Thread: Compressor ID and cap tube sizing

  1. #1
    Join Date
    Apr 2004
    Location
    Minnesnowta
    Posts
    2,364
    Post Likes
    Can anybody help with sizing capillary tubes for two Matsushita compressors? It's a long story, but this is a class project and the compressors were pulled from refrigerators, oil changed, and new unit being built from scratch. Converting from R-12 to R-134a. Targeting a -10 degree evap.
    Model #1: CB120L26
    LRA: 15.1Amps

    Model #2: DA66L11RAU6
    LRA: 11.3Amps

    I've been to the Panasonic web site and to the J/B Ind. web site but to no avail. Also put in a call to Matsushita but they were of no help. Thanks for any info.
    Wisdom has been chasing you, but you have always been faster.

    In your darkest hour, when the demons come, call on me brother and we shall fight them together.

    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  2. #2
    Join Date
    Apr 2004
    Location
    Minnesnowta
    Posts
    2,364
    Post Likes
    Thread Starter
    As long as we're on this topic, can you tell me what a model number on a comnpressor out of a Dixie-Narco vending machine means? Compressor model # is E5187A2170G20. This is part of my previous post. Thanks
    Wisdom has been chasing you, but you have always been faster.

    In your darkest hour, when the demons come, call on me brother and we shall fight them together.

    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  3. #3
    Join Date
    Aug 2002
    Posts
    6,047
    Post Likes
    I had an old neighbor, may God rest his soul. That dear man was around doing this work when Seal Units Parts Company was just starting out.
    If anybody would be able to give you a heads up, I would say it would be Supco.

    If this doesnt help, post back and I'll dig around with you. We'll figure this out.

  4. #4
    Join Date
    Apr 2004
    Location
    Minnesnowta
    Posts
    2,364
    Post Likes
    Thread Starter
    Thanks Dichlorodifluoromethanerules. I'll let you know.
    Wisdom has been chasing you, but you have always been faster.

    In your darkest hour, when the demons come, call on me brother and we shall fight them together.

    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  5. #5
    Join Date
    Aug 2002
    Posts
    6,047
    Post Likes
    Originally posted by doc havoc
    Thanks Dichlorodifluoromethanerules. I'll let you know.

    That's funny! That's the first time anyone here has called me "by that name"!

    Keep me informed. Maybe I can learn a lesson myself in reseach preceedures with this adventure.

    By the way, have you searched for the manufacturer using the Thomas Registry? They list ALL manufacturers. And perhaps The News would have a referance for them in their yearly directory. I dont know if your a member of their listing.

    You might consider e-mailing someone over there at The News and making inquiry.

    [Edited by R12rules on 10-07-2004 at 12:46 PM]

  6. #6
    Join Date
    Jun 2004
    Location
    Baltimore
    Posts
    18
    Post Likes
    I searched through my Matsushita file and couldn't come up with much info. All I found was that a compressor with a very similar model number to your second one put out 735 Btu/h at -10/130.

    In this change over are you changing all refrigeration components. I ask because you can sometimes run into problems on R-134a swaps on cap tube systems. As I understand it R-12 and the mineral oil in an R-12 system leave a benign varnish on the inside of the copper tubing and just sits there and does nothing for years. Then when you change over to R-134a you also have to change to POE oil. This oil actually disolves this once benign varnish into solution and then it comes out of solution when the liquid refrigerant starts to become a gas which, unfortunately, is in your cap tube. Therefore resulting in a plugged cap tube. This is not always the case, in fact usually not the case but it does happen and is something you should be aware of when making changes from R-12 to R-134a. We usually tell people with cap tube systems to use one of the many drop-in replacement refrigerants which do not require POE oil just in case.

    Danfoss AE

  7. #7
    Join Date
    May 2004
    Posts
    14,135
    Post Likes

  8. #8
    Join Date
    Apr 2004
    Location
    Minnesnowta
    Posts
    2,364
    Post Likes
    Thread Starter
    Danfoss Engineer, yes we do change all the tubing. I don't think we do an adequate job of flushing oil out of the compressor though. My last price quote for POE oil was $45.00/gallon so we do tend to skimp on waste. Is there another way to flush oil from compressor? We drain it, measure the amount and fill with new oil. Maybe I'm missing a step?
    Wisdom has been chasing you, but you have always been faster.

    In your darkest hour, when the demons come, call on me brother and we shall fight them together.

    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  9. #9
    Join Date
    Apr 2004
    Location
    Minnesnowta
    Posts
    2,364
    Post Likes
    Thread Starter
    Lusker, thanks for the reply. Those charts are the same ones we use in class, unfortunately the lowest HP on these charts is 1/8 HP. One of the compressors in question is only about 735 BTUH at -10 evap. That's smaller than 1/12 horsepower if I calculated correctly.
    Wisdom has been chasing you, but you have always been faster.

    In your darkest hour, when the demons come, call on me brother and we shall fight them together.

    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  10. #10
    Join Date
    Jun 2004
    Location
    Baltimore
    Posts
    18
    Post Likes
    Originally posted by doc havoc
    I don't think we do an adequate job of flushing oil out of the compressor though. My last price quote for POE oil was $45.00/gallon so we do tend to skimp on waste. Is there another way to flush oil from compressor? We drain it, measure the amount and fill with new oil. Maybe I'm missing a step?
    I thought $45/gallon was absurd until I checked my own price book. Our list price is $333.52/gallon LOL! You'd think we were selling fancy Champagne or something. As for your technique that's fine. Just get as much out as possible by draining it out of the suction port. The little left over shouldn't cause any problems.

    Lusker, thanks for the reply. Those charts are the same ones we use in class, unfortunately the lowest HP on these charts is 1/8 HP. One of the compressors in question is only about 735 BTUH at -10 evap. That's smaller than 1/12 horsepower if I calculated correctly.
    You can directly convert Btu/h into horsepower but that doesn't give you anything useful. Compressor horsepower was something that was used back when compressors were belt driven by external electric motors. This practice still lingers today but there is no way to directly compare motor horsepower to refrigeration capacity since it depends on the efficiency of the pump. I believe most compressor manufacturers list a nominal horsepower for their compressors that roughly equates to the power needed at air-conditioning conditions. At LBP conditions the refrigeration capacity for the same motor would be greatly reduced. So we at Danfoss would call a compressor capable of 735 Btu/h @ -10 a 1/5 or 1/4 "horsepower" compressor. Since there's no established way of determining horsepower for compressors it's left up to the compressor manufacturers to determine and therefore Danfoss, Tecumseh and Copeland all have slightly different definitions of "horsepower". I know referring to horsepower is still very prevalent today but the correct way is by Btu/h or tons.

    Danfoss AE

  11. #11
    Join Date
    Aug 2002
    Posts
    6,047
    Post Likes
    Mr. Danfoss,

    What is your recomended method for removing the oil from a pot compressor.

    In another thread, I aproached a NuCalgon rep at a wholesale house. He had some very interesting advice given him from the factory tech support person he phoned on my behalf.

    ....Something about drilling tek screws down the side of the can until oil squirts out....

    Those stiff plastic tubes will not always insert into the service port.
    It is not always practical to "tip" the condensing unit in order to remove the oil either.

    I have even heard advice that we are to leave things be unless the compressor should be replaced.
    Replaced either because the POE oil is contaminated with moisture or replaced due to ineffecient compressor.


    Shux, if it was up to me, I'd just weld in a short piece of tubing from the base of the compressor and have it extend out to where a field service tech could un-screw a 1/4" flare cap, attach a service hose and pressure the oil out into a measuring cup.

    What's six or eight inches of tubing going for these days?
    And how long would it take to punch just one more hole into a steel housing?
    And what would be the added expence of just one more weld onto the side of a pot compressor?

    Honestly, we in the field could pretty much care less about those low side ports you factory people pinch off near the top of the cans.
    In most cases, we simply leave them alone and ignore em'.

    If you gave us one we could use ... I imagine everyone would be buying your particular brand of compressor rather than the others .... simply because they were serviceable!

    We love service-able!


    Any comment? Thanks

  12. #12
    Join Date
    Jun 2004
    Location
    Baltimore
    Posts
    18
    Post Likes
    I honestly don't have much advice. For the fractional compressors just unbolt it and hang it upsidedown until all the oil drains out of the suction port. I know our newer scrolls have an oil drain connection (1/4" flare) that has an internal tube that goes to the sump so all you need to do if put a couple pounds of pressure in the crankcase and it all comes pumping out for you. On the Maneurop compressors you could just simply unbolt the oil sightglass. Most would come out right there and then it's easy to access the sump to get the remaining oil out. Make sure you get a new oil sight glass gasket!

    As for drilling holes and such I can't imagine that's ever a good idea. Who knows where those metal bits will end up.

    I imagine everyone would be buying your particular brand of compressor rather than the others .... simply because they were serviceable!
    Unfortunately I doubt it. Our customers, the OEM's, wouldn't pay for that feature and most don't really consider the compressor a service item. They would also prefer you to just buy a new compressor for obvious rea$on$. In the end though of the millions of compressors we sell there's probably some astronomically small percentage that need to get their oil changed for service reasons.

    Danfoss AE

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •