Page 2 of 2 FirstFirst 12
Results 14 to 18 of 18
  1. #14
    Join Date
    Mar 2008
    Location
    northern Indiana
    Posts
    114
    I suggest a data logger on EWT & LWT you need some exact numbers.
    You are making too many assumptions. It sounds like a water problem be it temp, flow, or fouling.

  2. #15
    Join Date
    Apr 2005
    Location
    Boulder,CO.
    Posts
    539
    Is this system just Geo or do you have a cooling tower, If it's just geo sounds like you don't have enough tube in the ground, or if it has a tower I would lower your water temp.
    We don't ever let it get higher than 90deg.

  3. #16
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,417
    Quote Originally Posted by teeball57 View Post
    I suggest a data logger on EWT & LWT you need some exact numbers.
    You are making too many assumptions. It sounds like a water problem be it temp, flow, or fouling.
    yep, seen it a million times
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  4. #17
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,417
    Quote Originally Posted by controldude View Post
    Is this system just Geo or do you have a cooling tower, If it's just geo sounds like you don't have enough tube in the ground, or if it has a tower I would lower your water temp.
    We don't ever let it get higher than 90deg.
    both scenarios are the common reason customers don't like water scource and have issues. there is a lack of engineering and design in the loop.
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  5. #18
    Join Date
    Jan 2007
    Location
    USA
    Posts
    13

    Trane WSHP

    What you are describing looks to me like a combination of high EWT and low flow.
    A typical wshp setup runs about a 10-11 degree delta T on the water temperatures when in cooling.
    Some people like to push for 15 degrees but you don't get much more cooling from that slower water flow and the compressor power consumtion increases. That means the compressor is working harder = higher head pressure.
    This summer continues to be a tough one on cooling equipment. High ambient temps, water temps and EAT are killing WSHP all over the country.
    If the EWT is toward the top end of the unit tolerance (95 EWT is higher than average)you can compensate by increase the water flow rate. Yeah, this increases loop pump power consumption but will reduce nuisance trips on the units.
    This is going on the idea the unit is OK for service.