I suggest a data logger on EWT & LWT you need some exact numbers.
You are making too many assumptions. It sounds like a water problem be it temp, flow, or fouling.
-
07-26-2012, 10:51 PM #15
Is this system just Geo or do you have a cooling tower, If it's just geo sounds like you don't have enough tube in the ground, or if it has a tower I would lower your water temp.
We don't ever let it get higher than 90deg.
-
07-27-2012, 12:32 PM #16
-
07-27-2012, 12:33 PM #17
-
08-16-2012, 01:31 PM #18
Regular Guest
- Join Date
- Jan 2007
- Location
- USA
- Posts
- 13
Trane WSHP
What you are describing looks to me like a combination of high EWT and low flow.
A typical wshp setup runs about a 10-11 degree delta T on the water temperatures when in cooling.
Some people like to push for 15 degrees but you don't get much more cooling from that slower water flow and the compressor power consumtion increases. That means the compressor is working harder = higher head pressure.
This summer continues to be a tough one on cooling equipment. High ambient temps, water temps and EAT are killing WSHP all over the country.
If the EWT is toward the top end of the unit tolerance (95 EWT is higher than average)you can compensate by increase the water flow rate. Yeah, this increases loop pump power consumption but will reduce nuisance trips on the units.
This is going on the idea the unit is OK for service.